Has anyone ever considered a vacuum or dry pressure test of a dry riser to check for leaks rather than carrying out a wet test?
Would this be considered a suitable alternative?
We're not Brazil we're Northern Ireland.

Offline SandDancer

  • Newbie
  • *
  • Posts: 29
Re: Service of Dry Risers
« Reply #1 on: November 25, 2010, 12:33:26 PM »
It may be an option, but care must be took with the construction material of the riser making sure it can  withstand a vacuum pressure rather than a straight pressure test as you may collapse the pipework!

Also something at the back of my addled brain is telling me that water needs to be used,  if not, joints can dry out and fail  ???


Offline AnthonyB

  • Firenet Extinguisher Expert
  • Global Moderator
  • Hero Member
  • *****
  • Posts: 2480
    • http://www.firewizard.co.uk
Re: Service of Dry Risers
« Reply #2 on: November 25, 2010, 03:48:39 PM »
I have heard in the past of testing under gas pressure, but I'm not sure if it was air or a special mixture - never seen this first hand though, only water testing.
Anthony Buck
Owner & Fire Safety Consultant at Fire Wizard


Extinguisher/Fire History Enthusiast

Fire Extinguisher Facebook Group:
http://www.facebook.com/group.php?gid=65...415&ref=ts
http://www.youtube.com/user/contactacb
https://uk.linkedin.com/in/anthony-buck-36

Offline SeaBass

  • Full Member
  • ***
  • Posts: 166
Re: Service of Dry Risers
« Reply #3 on: November 25, 2010, 04:33:39 PM »
Air pressure can be used for static testing but not dynamic flow rates, which are just as important. If air pressure testing is used, pressure relief valves need to be included in the pressurisation equipment to prevent any risks arising from over pressurisation of the riser pipe work and valves. Most risers also have AAVs at the head of the pipe work which are designed to vent air from the system. This complicates air pressure testing.
I think that the joints that SandDancer is referring to are Vitriolic joints which are found in wet risers and sprinkler systems rather than dry risers.