The question was specifically about the boxes. The actual door releases are usually tested during the weekly fire alarm test, a MCP is tested the alarm goes off and people ensure that the doors unlock. I raised the question as to whether there was a test routine for the actual box to that it would operate independantly of the alarm. Afterall the aim of the box is to release the door, if it fails to release with the alarm. As such I feel it should be tested independantly and the results recorded.
So I did answer your question correctly and precisely, Mike. I wouldn't want to quote BS recommendations which are not strictly relevant.
The only recommendation in BS7273-4 for testing the Emergency Door Release switch (green box) is that it is carried out every year. The weekly test recommendation only mentions using a fire alarm signal to ensure the door release mechanism operates and has no mention of the EDR.
Personally, I feel that once a year is nowhere near often enough for such an important part of the system.
Interestingly, the weekly test is under the heading of Routine Testing, whilst the annual testing of EDRs is under the heading Inspection and Testing. With the latter being carried out by a 'competent' person.
I can't see why the Routine Testing (presumably carried out by premises staff) shouldn't include the EDR, so that it is tested weekly. But this is only my opinion and not the BS recommendation. They obviously don't consider the EDR as important as the other equipment on the fire signal path in ensuring the correct operation of the door release mechanism.