As your system - to my understanding - is essentially a 5839 pt 6 system then you would also normally need 72 hour battery standby capacity.
I think it should be a part 1 system because kernow stated “i recently viewed a grade A fire alarm in
a new build block of residential flats”.
If you check out clause
1. Scope in Part 6 it defines what is included and what is not included.
This part of BS 5839 applies to forms of dwelling including bungalows, multi-storey houses, individual flats and maisonettes, mobile homes, sheltered houses, housing providing NHS supported living in the community (as defined in Health Technical Memorandum 88 [1]), mansions, and
houses divided into several self-contained single-family dwelling units. It does not apply to hostels, caravans or boats (other than permanently moored boats used solely as residential premises),
or to the communal parts of purpose-built sheltered housing and blocks of flats or maisonettes.
I accept a dedicated fuse board is not required in most cases but what about the following?
25.2 (a) Where the user requires to isolate the building during closed hours,
a separate supply should be provided for the fire alarm system that should not normally be isolated during closed hours.
25.2 (b) It is not acceptable for the electricity supply to be connected via a card or coin operated meter or similar device.