insurance void if hardwired electrics not inspected&tested
« on: July 01, 2011, 09:29:50 AM »
hi
on looking at the recommended frequency of electrical installations on commercial proerties
in the event of fire would the buildings insurance policy be null and void if no inspection/test had been carried out
(ie laundrette 1 year recommended frequency,which has had no inspection/test for over 5 years)???
would this be an easy get out for any insurance company, in that the building  would be seen
as not to have been maintained to current standards/legislation ,(electrical reg's)

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: insurance void if hardwired electrics not inspected&tested
« Reply #1 on: July 01, 2011, 10:27:37 AM »
Possibly if it was shown that a fire was caused as a result of an electrical fault that would have been discovered and rectified had the inspection been carried out.

Offline nearlythere

  • Hero Member
  • *****
  • Posts: 4351
Re: insurance void if hardwired electrics not inspected&tested
« Reply #2 on: July 01, 2011, 11:01:51 AM »
The insurance company could use the Contributory Negligence arguement.
We're not Brazil we're Northern Ireland.

Offline John Webb

  • Hero Member
  • *****
  • Posts: 838
Re: insurance void if hardwired electrics not inspected&tested
« Reply #3 on: July 01, 2011, 11:12:22 AM »
Interestingly the current BS7671:2008 "Wiring Regs" does not specifically lay down frequency of testing of fixed installations.

It is the IEE's 'Guidence Note 3 - Inspection and Testing' which lists a large number of occupancies and which says the Launderettes should be tested yearly. There are cross references to both the Electricity at Work Regulations and the Electricity, Safety, Quality and Continuity Regs. I think it is the former Regs (Regulation 4 and Memorandum) which may be the legal requirement.

So if you haven't complied with statutory requirements could that be a get-out for the insurer?

(By the way, the new version of BS7671:2011 17th Edition with Amendment 1 is to be published this month. Taking effect from 1st Jan 2012, the 'Periodic Testing' is one area undergoing significant changes - it will now be known as the Electrical Installation Condition Report with better recording of the tests carried out with a simplification of the codes indicating if the installation is dangerous or not.)
John Webb
Consultant on Fire Safety, Diocese of St Albans
(Views expressed are my own)

Offline colin todd

  • Hero Member
  • *****
  • Posts: 3473
  • Civilianize enforcement -you know it makes sense.
    • http://www.cstodd.co.uk
Re: insurance void if hardwired electrics not inspected&tested
« Reply #4 on: July 03, 2011, 06:01:36 PM »
Most unlikely unless there was a warranty in the policy.
Colin Todd, C S Todd & Associates