Author Topic: Emergency Lighting Generators.  (Read 13466 times)

Offline Tom Sutton

  • Hero Member
  • *****
  • Posts: 2287
Emergency Lighting Generators.
« on: July 07, 2011, 03:44:15 PM »
Quote
Re BS5266-1:2005 Would the fact that we have a generator to power all amenaties should we suffer a power failure, that kicks in within seconds cover us for the emergency lighting.

I would imagine the answer is yes providing it conforms to the above standard an kicks in between 5 and 15 secs but I would like it confimed. Please  :-*
All my responses only apply to England and Wales and they are an overview of the subject, hopefully it will point you in the right direction and always treat with caution.

Offline Davo

  • Hero Member
  • *****
  • Posts: 1144
Re: Emergency Lighting Generators.
« Reply #1 on: July 07, 2011, 07:26:40 PM »
Hi Tom

As you know, there are different types of EL eg escape or for machinery etc
So it would depend on what the premises are used for imo.

In a factory with lathes etc my answer would be no, in an office then perhaps

The problem with gennys is that you have to test them on load, maintenance etc, so EEL might be cheaper in the long run.

davo

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: Emergency Lighting Generators.
« Reply #2 on: July 07, 2011, 07:29:06 PM »
Will it be sensitive to lighting sub circuit failure? How are the lighting circuits subdivided? Whilst your description works for full mains failure if a primary lighting MCB trips because of a fire will key areas be left in darkness? There is a difference between emergency lighting and escape lighting.

Offline colin todd

  • Hero Member
  • *****
  • Posts: 3473
  • Civilianize enforcement -you know it makes sense.
    • http://www.cstodd.co.uk
Re: Emergency Lighting Generators.
« Reply #3 on: July 07, 2011, 10:37:33 PM »
Big Al.

Escape lighting is a form of emergency lighting. What I think you meant to say is that there is a distinction between escape lighting and standy lighting.
Colin Todd, C S Todd & Associates

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: Emergency Lighting Generators.
« Reply #4 on: July 07, 2011, 11:18:01 PM »
Thanks Col. Thats probably what I meant. Love the irony though. ;)

Offline Phoenix

  • Hero Member
  • *****
  • Posts: 677
  • Get a bicycle. You will not live to regret it
    • MetaSolutions (Fire Safety Engineering) Ltd.
Re: Emergency Lighting Generators.
« Reply #5 on: July 08, 2011, 09:18:19 AM »

Quote
Re BS5266-1:2005 Would the fact that we have a generator to power all amenaties should we suffer a power failure, that kicks in within seconds cover us for the emergency lighting.

I would imagine the answer is yes providing it conforms to the above standard an kicks in between 5 and 15 secs but I would like it confimed. Please  :-*

Many premises have areas where it would not be safe for people to be plunged into darkness for 15 seconds, eg factories, hospitals, kitchens and what about staircases.  Because of that and because the generators don't usually kick in at all if it is only the lighting circuit that fails, it is normally important that conventional emergency lighting of some sort is provided in addition to the cover provided by the generator. 

Having said that, it may be possible to relax on the conventional emergency lighting in less critical areas.

Stu


Offline Tom Sutton

  • Hero Member
  • *****
  • Posts: 2287
Re: Emergency Lighting Generators.
« Reply #6 on: July 08, 2011, 10:25:38 AM »
My posting was based on BS 5266, see below, but I imagine it would be very unlikely to meet the standards therefore it needs surveying by a competent person and I suspect the outcome would be the provision of a separate emergency escape route lighting system.

4.6 Standby lighting
If standby lighting is used to provide emergency escape lighting, the installation shall comply with the provisions of this standard and the appropriate product and wiring standards.

4.2.6 Response time: The emergency lighting detailed in this code should be provided within 5 s of the failure of the normal lighting supply, but at the discretion of the enforcing authority this period can be extended to a maximum of 15 s in premises likely to be occupied for the most part by persons who are familiar with them and the escape routes.
All my responses only apply to England and Wales and they are an overview of the subject, hopefully it will point you in the right direction and always treat with caution.

Offline AnthonyB

  • Firenet Extinguisher Expert
  • Global Moderator
  • Hero Member
  • *****
  • Posts: 2493
    • http://www.firewizard.co.uk
Re: Emergency Lighting Generators.
« Reply #7 on: July 08, 2011, 07:05:16 PM »
In my experience emergency generators are used a business continuity measure providing standby lighting, essential services power and IT (to back up local UPS to servers that has a quicker changeover) and that escape routes and high hazard task areas still have self contained battery fittings (NM or M as required) on local circuits for escape/safety purposes.

In other words, I echo the above posts! :D
Anthony Buck
Owner & Fire Safety Consultant at Fire Wizard


Extinguisher/Fire History Enthusiast

Fire Extinguisher Facebook Group:
http://www.facebook.com/group.php?gid=65...415&ref=ts
http://www.youtube.com/user/contactacb
https://uk.linkedin.com/in/anthony-buck-36

Offline lyledunn

  • Hero Member
  • *****
  • Posts: 503
Re: Emergency Lighting Generators.
« Reply #8 on: October 30, 2011, 06:31:06 PM »
Problem is that the generator will probably feed in to the same circuits as the normal supply. Thus a fault that took out the normal supply might also take out the gen. If on the other hand the gen supplies slave luminaires then the circuits would have to be of appropriate fire resistance, mims, fire tuff or the like.

Offline CivvyFSO

  • Hero Member
  • *****
  • Posts: 1583
Re: Emergency Lighting Generators.
« Reply #9 on: October 31, 2011, 12:11:04 PM »
It's all very good until a fire burns through a main lighting cable, taking the lighting out without taking the power supply out. Hey presto - Complete darkness.

Might as well go the whole hog and accept the fire as a light source under risk assessment.  ;D


Offline AnthonyB

  • Firenet Extinguisher Expert
  • Global Moderator
  • Hero Member
  • *****
  • Posts: 2493
    • http://www.firewizard.co.uk
Re: Emergency Lighting Generators.
« Reply #10 on: October 31, 2011, 11:04:41 PM »
Well indeed - and the same can be said for some central battery systems, although both can monitor local circuits for failure as well if correctly set up.

If it's a slow starting generator (> 5 seconds) you need separate emergency lighting anyway.

All of which is why you don't see many generator only EL systems.
Anthony Buck
Owner & Fire Safety Consultant at Fire Wizard


Extinguisher/Fire History Enthusiast

Fire Extinguisher Facebook Group:
http://www.facebook.com/group.php?gid=65...415&ref=ts
http://www.youtube.com/user/contactacb
https://uk.linkedin.com/in/anthony-buck-36