Author Topic: Corridor Ventilation  (Read 8478 times)

Offline GB

  • Full Member
  • ***
  • Posts: 234
Corridor Ventilation
« on: August 29, 2011, 11:14:58 AM »
Is the purpose of ventilators within the corridor adjoining a protected stair to provide make up air for the stair and stair vent or in fact to ventilate the corridor? I thought the former but I may be wrong :o

If so should the window be bottom or top hung?


Offline Tom Sutton

  • Hero Member
  • *****
  • Posts: 2287
Re: Corridor Ventilation
« Reply #1 on: August 29, 2011, 04:10:21 PM »
Check out http://fire.org.uk/forum/index.php?topic=1748.0 its about the BRE research report summary Smoke Ventilation of Common Access Areas of Flats and Maisonettes which I think would be relevant in all buildings. The report summary at http://www.bre.co.uk/filelibrary/pdf/rpts/partb/Smoke_Ventilation.pdf
All my responses only apply to England and Wales and they are an overview of the subject, hopefully it will point you in the right direction and always treat with caution.

Offline CivvyFSO

  • Hero Member
  • *****
  • Posts: 1583
Re: Corridor Ventilation
« Reply #2 on: August 29, 2011, 08:58:10 PM »
They are to ventilate the corridor.

Read the BRE report summary.

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: Corridor Ventilation
« Reply #3 on: August 29, 2011, 09:41:21 PM »
My simplistic summary would be thus.

Fires cause thermal expansion and convection  which create an increase in pressure at high levels within the room involved.
Fires usually occur in rooms and not in lobbies or staircases because we keep those areas clear of combustibles.
If a fire occurs in room the increase in pressure will push smoke and products of combustion out through the door and other openings into the space beyond  in an attempt to equalise the pressure.
If we put a vent in the lobby such increase in pressure will be released harmlessly from the vent  to the atmosphere and therefore smoke will not be pushed into the staircase.

In summary the vent is provided in the lobby to release the pressure and thus protect the staircase.

As people will open doors into the staircase as they escape it is possible smoke may enter the staircase as they leave, so the vent in the staircase will allow that to escape.

After all we would not want to source make up air for the staircase from the very location of the fire.
I know it is a gross over simplification but that is my understanding of the BRE report.

Offline CivvyFSO

  • Hero Member
  • *****
  • Posts: 1583
Re: Corridor Ventilation
« Reply #4 on: August 30, 2011, 01:08:40 PM »
I think that Kurnals explanation is particularly good, and it demonstrates why this vent is most certainly NOT make-up air for the stair vent.

Another way to look at it, ask colt whether they set their mechanical fans on 'suck' or 'blow' :)

Offline Tom Sutton

  • Hero Member
  • *****
  • Posts: 2287
Re: Corridor Ventilation
« Reply #5 on: August 30, 2011, 02:16:31 PM »
You mention, should the window be bottom or top hung, this being so I would think it is more likely to be there for the use by the FRS to improve working conditions when fighting the fire or clearing the smoke after a fire.
« Last Edit: August 30, 2011, 02:18:11 PM by Tom Sutton »
All my responses only apply to England and Wales and they are an overview of the subject, hopefully it will point you in the right direction and always treat with caution.

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: Corridor Ventilation
« Reply #6 on: August 30, 2011, 07:11:27 PM »
Bottom hung is recommended.