Author Topic: Means of Escape from Offices  (Read 3093 times)

jakespop

  • Guest
Means of Escape from Offices
« on: January 26, 2012, 10:34:52 AM »
Low to medium risk two storey offices in converted building with single staircase. Occcupants can escape to outside within 18 metres.
Is protected route required?  I would normally say No, dependent on risk and level of detection, but perhaps enclose any higher risk areas.
What concerns me is the section in blue guide which advises dead end conditions to be enclosed etc.  This would indicate all doors should be FD in this type of building.

Any opinions out there would be welcome.

Offline jokar

  • Hero Member
  • *****
  • Posts: 1472
Re: Means of Escape from Offices
« Reply #1 on: January 26, 2012, 10:39:07 AM »
Small premises guidance is in ADB but risk assess away.

Online AnthonyB

  • Firenet Extinguisher Expert
  • Global Moderator
  • Hero Member
  • *****
  • Posts: 2477
    • http://www.firewizard.co.uk
Re: Means of Escape from Offices
« Reply #2 on: January 27, 2012, 12:07:49 AM »
The guides do give the option of AFD in the rooms off an initial dead end instead of fire doors.
Anthony Buck
Owner & Fire Safety Consultant at Fire Wizard


Extinguisher/Fire History Enthusiast

Fire Extinguisher Facebook Group:
http://www.facebook.com/group.php?gid=65...415&ref=ts
http://www.youtube.com/user/contactacb
https://uk.linkedin.com/in/anthony-buck-36

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: Means of Escape from Offices
« Reply #3 on: January 27, 2012, 06:51:23 AM »
Have you considered the small building guidance in ADB or BS9999 / BS5588 part 11?
Is the 18m total distance of travel from furthest point, down the stairs to the final exit?

jakespop

  • Guest
Re: Means of Escape from Offices
« Reply #4 on: January 27, 2012, 02:45:37 PM »
Yes, travel distance within 18m to final exit!