Author Topic: removal of 1960's style doors within ground floor communal area  (Read 13878 times)

Offline Mar62

  • Full Member
  • ***
  • Posts: 207
removal of 1960's style doors within ground floor communal area
« on: February 10, 2012, 10:08:11 AM »
Views please. A ground and 5 upper storey, single staircase residential property has a ground floor with entrance front and rear. Gr floor is split into 3 parts, front lobby, central and rear lobby. Within the central lobby there is access to lift and the enclosed staircase, off of the front lobby there is access to two flats. They have recently had a brand new L3 system installed and all new E/L. Currently each lobby on the gr floor has AFD. Their request is this - can they remove the front set of doors and pannelling between the front and central lobby (to make it open), upgrade the two doorsets to the flats with FD30s and replace the doorset and pannelling between the central lobby and the rear lobby to 30 minute resistance? My only thought would be to make the doors to the flats FD60s instead. There are a lot of elderly people within the block and so any evacuation may be delayed or slow. Very minimal ignition sources within the communal area. Staircase totally sterile area. Opinions please?
Each and every day is a learning curve and today is one of those days?

Offline nearlythere

  • Hero Member
  • *****
  • Posts: 4351
Re: removal of 1960's style doors within ground floor communal area
« Reply #1 on: February 10, 2012, 10:32:30 AM »
Views please. A ground and 5 upper storey, single staircase residential property has a ground floor with entrance front and rear. Gr floor is split into 3 parts, front lobby, central and rear lobby. Within the central lobby there is access to lift and the enclosed staircase, off of the front lobby there is access to two flats. They have recently had a brand new L3 system installed and all new E/L. Currently each lobby on the gr floor has AFD. Their request is this - can they remove the front set of doors and pannelling between the front and central lobby (to make it open), upgrade the two doorsets to the flats with FD30s and replace the doorset and pannelling between the central lobby and the rear lobby to 30 minute resistance? My only thought would be to make the doors to the flats FD60s instead. There are a lot of elderly people within the block and so any evacuation may be delayed or slow. Very minimal ignition sources within the communal area. Staircase totally sterile area. Opinions please?
Is the separation between the front and central lobby Fire Resisting including the door? Does the lift and stairway areas on upper floor levels have flats opening directly onto it or is the stairway and lift within a FR enclosure off which are corridors or lobbys to flats?
« Last Edit: February 10, 2012, 10:39:01 AM by nearlythere »
We're not Brazil we're Northern Ireland.

Offline Mar62

  • Full Member
  • ***
  • Posts: 207
Re: removal of 1960's style doors within ground floor communal area
« Reply #2 on: February 10, 2012, 11:14:38 AM »
Hi NT. Very old doors with gaps between the leafs and pannelling dating back to 1960's.
Each and every day is a learning curve and today is one of those days?

Offline Mar62

  • Full Member
  • ***
  • Posts: 207
Re: removal of 1960's style doors within ground floor communal area
« Reply #3 on: February 10, 2012, 11:24:37 AM »
On the upper levels, the flats exit directly into a lobby where the lift is accessed and also opposite the lift is where the storey exit to the staircase is. 4 flats per floor. There is no internal lobby within the flats.
Each and every day is a learning curve and today is one of those days?

Offline nearlythere

  • Hero Member
  • *****
  • Posts: 4351
Re: removal of 1960's style doors within ground floor communal area
« Reply #4 on: February 10, 2012, 12:04:22 PM »
Hi NT. Very old doors with gaps between the leafs and pannelling dating back to 1960's.
Martin
Were, or are, the doors between the front and central lobby fire resisting self closing?
Are you sure the doors to the ground floor flats are not already fire resisting self closing?
« Last Edit: February 10, 2012, 03:08:27 PM by nearlythere »
We're not Brazil we're Northern Ireland.

Offline Mar62

  • Full Member
  • ***
  • Posts: 207
Re: removal of 1960's style doors within ground floor communal area
« Reply #5 on: February 10, 2012, 12:17:07 PM »
Unfortunately I have not been able to gain access to the flat to look at the doors yet, still trying to pursue that one but looking at them from the outside I would say that they are solid timber doors only without any fire resistance.

Both sets of the ground floor doors date back to the 1960's. Probably were designed to an older standard. Both sets are currently "double swing" but if the replacement doors are fitted they will be one direction only with self closers.
Each and every day is a learning curve and today is one of those days?

Offline nearlythere

  • Hero Member
  • *****
  • Posts: 4351
Re: removal of 1960's style doors within ground floor communal area
« Reply #6 on: February 10, 2012, 12:30:07 PM »
Unfortunately I have not been able to gain access to the flat to look at the doors yet, still trying to pursue that one but looking at them from the outside I would say that they are solid timber doors only without any fire resistance.

Both sets of the ground floor doors date back to the 1960's. Probably were designed to an older standard. Both sets are currently "double swing" but if the replacement doors are fitted they will be one direction only with self closers.
In older flats it may have been that the protection of the stairway was provided by two fire resisting doors between any flat and a stairway enclosure. It might be that above the ground floor this was provided within each flat by the provision of a FR lobby.
It is possible that on the ground floor the doors separating the front, central and rear lobbys where incorporated in this principle in that when you came down the stairs you could go either out through the front or the rear lobby from the central lobby which contains the stairway. The principle here being that when you are in the central lobby you had two fire doors between it and a flat. If there was only one way out of the stairway enclosure that escape route had to be protected from any flat by two fire doors. With two separate ways out you would use one if the other was unusable because of the weakness in the protection of the escape route.
Are there any plans? You might have to look for old ones which may have been used for the conversion to see what the design was or should have been.
We're not Brazil we're Northern Ireland.

Offline Mar62

  • Full Member
  • ***
  • Posts: 207
Re: removal of 1960's style doors within ground floor communal area
« Reply #7 on: February 10, 2012, 12:52:20 PM »
Thats exactly what I was thinking, (about entering the central lobby and having the choice of two directions). My main objection to them was regarding the loss of compartmentation between the flats entrances and the exit from the staircase. Would not replacing the two flat doors to FD30 or 60 help compensate for the removal of the set of doors as at present the ones in the lobby would do little to prevent any passage of smoke or flame?

I'll have to ask about plans but I very much doubt it. Until now this block has been very poorly looked after.
Each and every day is a learning curve and today is one of those days?

Offline nearlythere

  • Hero Member
  • *****
  • Posts: 4351
Re: removal of 1960's style doors within ground floor communal area
« Reply #8 on: February 10, 2012, 01:31:09 PM »
Thats exactly what I was thinking, (about entering the central lobby and having the choice of two directions). My main objection to them was regarding the loss of compartmentation between the flats entrances and the exit from the staircase. Would not replacing the two flat doors to FD30 or 60 help compensate for the removal of the set of doors as at present the ones in the lobby would do little to prevent any passage of smoke or flame?

I'll have to ask about plans but I very much doubt it. Until now this block has been very poorly looked after.
Not really. For the purpose of lobby protection the provision of one 60min door does not provide the protection of two 30min types.
You will probably find that in bygone eras, in NI anyway, the passage of smoke was not a big enough issue which could not be theoretically resolved by a good fitting door and fire resistance by upgrading door stops to 25mm glued and screwed to the frame or by adding 12.5 mm on to the existing 12.5mm stop. That's the way it was and I still see the remnants of that approach in places.
As you say it does sound like the building has not been kept up to date with regards to some fire safety issues but we are in the age of FRAs now and reviewing so as to keep them up to date. As you seem to have been asked a specific question I would be inclined to reserve judgment pending a full FRA as by their removal you could be downgrading the protection of the stairway from what was originally intended, whatever that was. You could maybe consider hold open devices if the landlord does not want a review carried out (thats his prerogative and his problem) but you might be best to include some form of comment on the standard of protection of the doors you have been asked to specifically deal with.
It is a little difficult to address this properly without seeing the building or a plan or having some history of what has gone on in the past.
We're not Brazil we're Northern Ireland.

Offline Mar62

  • Full Member
  • ***
  • Posts: 207
Re: removal of 1960's style doors within ground floor communal area
« Reply #9 on: February 10, 2012, 02:44:33 PM »
Ok well thanks very much for your time and for your help NT. Much obliged.
Each and every day is a learning curve and today is one of those days?

Offline Mar62

  • Full Member
  • ***
  • Posts: 207
Re: removal of 1960's style doors within ground floor communal area
« Reply #10 on: February 10, 2012, 02:50:07 PM »
PS. Yes I have mentioned Hold open devices but their wish is to make it nice and open plan????

Thanks
Each and every day is a learning curve and today is one of those days?

Offline nearlythere

  • Hero Member
  • *****
  • Posts: 4351
Re: removal of 1960's style doors within ground floor communal area
« Reply #11 on: February 10, 2012, 03:11:24 PM »
PS. Yes I have mentioned Hold open devices but their wish is to make it nice and open plan????

Thanks
"Their" being the occupants or the building owners? Are these are privately owned apartments managed by a committee of owners?
We're not Brazil we're Northern Ireland.

Offline Mar62

  • Full Member
  • ***
  • Posts: 207
Re: removal of 1960's style doors within ground floor communal area
« Reply #12 on: February 10, 2012, 04:04:01 PM »
yes " their" as in the residents committee and yes they own the block. They do employ a management agent who has only just taken over from another company.
Each and every day is a learning curve and today is one of those days?

Offline nearlythere

  • Hero Member
  • *****
  • Posts: 4351
Re: removal of 1960's style doors within ground floor communal area
« Reply #13 on: February 10, 2012, 04:13:39 PM »
yes " their" as in the residents committee and yes they own the block. They do employ a management agent who has only just taken over from another company.
I would probably suggest that the residents are unaware that the common areas are relevant premises and a FRA is required. Either one has not been done, or it has and they have decided to ignore it. I take it your building is in England or Wales somewhere?
We're not Brazil we're Northern Ireland.

Offline Mar62

  • Full Member
  • ***
  • Posts: 207
Re: removal of 1960's style doors within ground floor communal area
« Reply #14 on: February 10, 2012, 04:18:07 PM »
Central London. And yes they are going to get the FRA done asap. One was done about three years ago before all this was discussed.