Author Topic: Fire alarms in Bars  (Read 4034 times)

jakespop

  • Guest
Fire alarms in Bars
« on: May 05, 2012, 10:59:04 AM »
I have recently visited a Bar/Restaurant with fairly comprehensive fire alarm with AFD. However, bar was built some time ago and there are MCP's at bar/restaurant exits. MCP's behind bar presumably to discourage malicious activation in the past. As long as procedures are clear to staff is this acceptable?
I would appreciate opinions on acceptability or otherwise.

Offline Phoenix

  • Hero Member
  • *****
  • Posts: 677
  • Get a bicycle. You will not live to regret it
    • MetaSolutions (Fire Safety Engineering) Ltd.
Re: Fire alarms in Bars
« Reply #1 on: May 05, 2012, 12:45:53 PM »
Do you mean there are no MCPs at exits?

If so, that's ok.

Stu


jakespop

  • Guest
Re: Fire alarms in Bars
« Reply #2 on: May 05, 2012, 02:39:18 PM »
Well spotted, how a missed word can make such a difference. There are no MCP's at exits within bar/restaurant area.

Offline Phoenix

  • Hero Member
  • *****
  • Posts: 677
  • Get a bicycle. You will not live to regret it
    • MetaSolutions (Fire Safety Engineering) Ltd.
Re: Fire alarms in Bars
« Reply #3 on: May 05, 2012, 04:34:52 PM »
Not only is this ok, it is recommended (provided all procedures and training are ok, as you say).

Stu


Offline colin todd

  • Hero Member
  • *****
  • Posts: 3473
  • Civilianize enforcement -you know it makes sense.
    • http://www.cstodd.co.uk
Re: Fire alarms in Bars
« Reply #4 on: May 05, 2012, 08:59:08 PM »
Its fine and a recognized case for a variation under BS 5839-1.
Colin Todd, C S Todd & Associates