Author Topic: Fire prtection impairment notices  (Read 8439 times)

Offline mailkaz

  • Newbie
  • *
  • Posts: 8
Fire prtection impairment notices
« on: October 18, 2012, 06:30:25 PM »
Hi Guys

Just wondering if you could help with a query regarding fire protection impairment notices and whether there is a legal application/requirement under the RRFSO

Thanks in advance
HM

Offline Phoenix

  • Hero Member
  • *****
  • Posts: 677
  • Get a bicycle. You will not live to regret it
    • MetaSolutions (Fire Safety Engineering) Ltd.
Re: Fire prtection impairment notices
« Reply #1 on: October 19, 2012, 12:21:04 AM »
Any impairment to a fire safety system is an alteration that will be relevant under the RR(FS)O.  The requirements of the Order must continue to be met (possibly by some compensatory feature) while the system is impaired.  What is the nature of the impairment and what fire safety provision will it affect?

Stu


Offline mailkaz

  • Newbie
  • *
  • Posts: 8
Re: Fire prtection impairment notices
« Reply #2 on: October 19, 2012, 12:41:25 AM »
Many thanks for your reply.

Cheers
HM

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: Fire prtection impairment notices
« Reply #3 on: October 19, 2012, 07:38:46 AM »
They are ususally seen as enforcement with a small E where the  fire service think there is a  reasonable likelihood that the RP will comply without the big stick of an enforcement notice. Failure to comply with an enforcement notice is an offence. Failure to comply with a notice of impairment  , in itself, is not.

The fire service like the impairment notice because it in in accordance with the enforcement concordat and it means that they dont have to come back in any particular timescale to make sure you have complied. They will usually trust you to do it before their next audit cycle.

Offline mailkaz

  • Newbie
  • *
  • Posts: 8
Re: Fire prtection impairment notices
« Reply #4 on: October 19, 2012, 08:15:05 AM »
Thank you phoenix, kurnal,

I am grateful for the replies, which confirms my understanding of impairment notices.

Thank you
Cheers
HM

Offline wee brian

  • Administrator
  • Hero Member
  • *****
  • Posts: 2425
Re: Fire prtection impairment notices
« Reply #5 on: October 19, 2012, 09:57:35 AM »
So, its not really a legal notice then?  Just a letter dresssed up a bit?


Midland Retty

  • Guest
Re: Fire prtection impairment notices
« Reply #6 on: October 22, 2012, 11:18:35 AM »
Well no, some brigades call them 'impairment notices', others simply send you a report listing deficiences found during their audit.

They are both the same thing.

Failure to comply with the contents of an impairment notice / report may lead to the issue of an enforcement notice.

Failing then to comply with an enforcement notice would be an offence.

Offline wee brian

  • Administrator
  • Hero Member
  • *****
  • Posts: 2425
Re: Fire prtection impairment notices
« Reply #7 on: October 22, 2012, 11:58:11 AM »
Interesting, thanks

So an "improvement Notice" requires you to improve something. But an "Impairment Notice" doesn't require you to Impair something, and its not really a notice.

You learn a new thing everyday