Author Topic: Penetration of Plastic Pipes  (Read 5750 times)

jakespop

  • Guest
Penetration of Plastic Pipes
« on: November 01, 2012, 05:31:18 PM »
I am finding numerous premises with plastic drainage pipes which penetrate floors and ceilings. Where these are enclosed at both levels I would be happy but I have recently found soil pipes in a hotel which go from a bedroom down into a garage. The bedroom has FD 30S door and there is L2 AFD.
 I would appreciate views and opinions of colleagues on whether they would expect intumescent collars or similar in this and similar instances.

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: Penetration of Plastic Pipes
« Reply #1 on: November 01, 2012, 06:11:52 PM »
Jakespop Have you considered the guidance in Approved Document B3- section 10 ?

Offline wee brian

  • Administrator
  • Hero Member
  • *****
  • Posts: 2424
Re: Penetration of Plastic Pipes
« Reply #2 on: November 05, 2012, 01:03:56 PM »
Have a look at the ASFP guide for risk assessors - you'll find some useful stuff in there

Offline JimK

  • Newbie
  • *
  • Posts: 11
Re: Penetration of Plastic Pipes
« Reply #3 on: November 29, 2012, 04:00:33 PM »
I think that if you use approved document Part B you want Section B3, Table 3, for pipes passing through a fire separating element.