Author Topic: BS 9999 Review  (Read 25168 times)

Offline Dinnertime Dave

  • Hero Member
  • *****
  • Posts: 819
Re: BS 9999 Review
« Reply #15 on: November 23, 2012, 03:00:05 PM »
one item that has been brought to my attention is -

4.2 Variation of guidance

The guidance on means of escape in Section 5 permits variations to be made to travel distances and door and/or stair widths on the basis that the level of risk can be reduced by the provision of additional fire protection measures. Such measures include an increased level of management of fire safety, the provision of an automatic sprinkler system, the provision of a smoke management system or the provision of an additional level of automatic fire detection.

I believe the items in bold are mentioned here only and no other reference to this in the document

Offline Phoenix

  • Hero Member
  • *****
  • Posts: 677
  • Get a bicycle. You will not live to regret it
    • MetaSolutions (Fire Safety Engineering) Ltd.
Re: BS 9999 Review
« Reply #16 on: November 23, 2012, 07:20:14 PM »
Well spotted DD.  These elements of the overall fire safety package may contribute to an assessment of the level of safety but, as far as the BS9999 guidance goes, no variation may be made because of them as claimed here.

Offline Phoenix

  • Hero Member
  • *****
  • Posts: 677
  • Get a bicycle. You will not live to regret it
    • MetaSolutions (Fire Safety Engineering) Ltd.
Re: BS 9999 Review
« Reply #17 on: November 23, 2012, 07:23:26 PM »
Incidentally, kurnal, if you want alternative suggestions for wordings, in light of wee brian's comment, I can provide.

Stu

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: BS 9999 Review
« Reply #18 on: November 23, 2012, 07:57:07 PM »
Stu I would be grateful if you would. I /We could obtain and use the BSI standard response form - though its not been issued yet for 9999 we could use one from a previous consultation. That would save a lot of time and deadline bashing later.