Author Topic: Your opinions please - fire alarm system offline  (Read 20690 times)

Midland Retty

  • Guest
Your opinions please - fire alarm system offline
« on: November 22, 2012, 06:28:33 PM »
I'm often accused (perhaps rightly so) of having an "OCD" when it comes to fire alarm systems that are offline in sleeping accomodation (hotels, HMOs, Care homes etc etc).

Lets say we have a HMO, fire alarm system is showing a general or undefiuned fault, functionality of system is unknown. Lets also assume it 6 o'clock on a friday afternoon.

Landlord does have a nominated fire alarm contractor but they can't get to site earliest until the following day.

The landlord is contactable by phone, but can't get to premsies to implement some form of temporary measures as s/he is abroad on holiday.

What do you feel is reasonable in this situation?

I for example would ask that the faults are inspected by a fire alarm engineer same-day to ascertain functionality of system (and restore acceptable level of functionality to the system where necessary).

If thats not possible I'd ask the landlord to implement temp measures in place to compensate for the non functioning alarm system, be it the installation of battery powered smoke alarms (if appropriate) conducting fire patrols, or even paying for tenants to stop in hotel overnight. All of these can be impracticable if landlord has no support and can't get to site, or if tenants are beligerant and dont want to be rehoused!.

Am I being 'over the top' ? I'd welcome your thoughts / opinions on this type of situation... what would you accept / recommend? Would you allow the system to remain offline overnight?

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: Your opinions please - fire alarm system offline
« Reply #1 on: November 22, 2012, 07:10:24 PM »
It isnt difficult to assess the functionality of the system. Thats got to be a first step. Test it.

But you are right and I go along with what you say. It is more common than you think. If a panel fails and is beyond repair, even a straight swap of panels can take more than a day.

There was one large hotel in a tourist area where they had ordered a completely new fire alarm system. What did the installer do first? Took out the old system completely then knocked off for three days (bank holiday). They got an august bank holiday prohibition notice as soon as one of the guests complained to the brigade.

If the system is completely down I like you would apply a risk based approach. Insist on the attendance of engineers to repair it if at all possible, many work 24/7. If this could not be achieved I would then consider how big? how many? who?  how much? how high? compartmentation? I also would look at smoke alarms and if not interconnected, back it up with waking patrols.

(I might even put in 8 extinguishers at each fire point as well  ;)  )

Midland Retty

  • Guest
Re: Your opinions please - fire alarm system offline
« Reply #2 on: November 23, 2012, 11:26:40 AM »
Thanks Kurnal

With regard to testing the functionality. How do you do that? Do you go around testing each call point and detector?

For example - worst case- a HMO, some of the tenants are out, you can't get in their rooms to look at the detection.

 
« Last Edit: November 23, 2012, 01:09:46 PM by The Manic Midlander »

Offline lancsfirepro

  • Full Member
  • ***
  • Posts: 175
Re: Your opinions please - fire alarm system offline
« Reply #3 on: November 23, 2012, 11:56:06 AM »
Quote from BS5839-1

46.3 Recommendations for arrangements for repair of faults or damage
The following recommendations apply.
a) Where maintenance is carried out by a third-party, such as a fire alarm maintenance organization, there should be an agreement for emergency call out to deal with any fault or damage that occurs to the system. The agreement should be such that, on a 24 h basis, a technician of the maintenance organization can normally attend the premises within eight hours of a call from the user.


I would argue that if the alarm maintenance company cannot adhere to this they are not providing a suitable system of maintenance.

Midland Retty

  • Guest
Re: Your opinions please - fire alarm system offline
« Reply #4 on: November 23, 2012, 01:12:03 PM »
Quote from BS5839-1

The agreement should be such that, on a 24 h basis, a technician of the maintenance organization can normally attend the premises within eight hours of a call from the user.[/i]

I would argue that if the alarm maintenance company cannot adhere to this they are not providing a suitable system of maintenance.

Agreed but often many landlords I deal with employ contractors loosely and dont have any formal agreements in place. Furthermore if the contractor is self employed s/he may legitimately be engaged on other calls and may genuinely be unable to attend.

Offline Wiz

  • Hero Member
  • *****
  • Posts: 1591
Re: Your opinions please - fire alarm system offline
« Reply #5 on: November 23, 2012, 02:16:00 PM »
I would suggest that a suitable simple test may be to operate at least one mcp and detector in each zone and, if possible, to choose devices towards the end of each zone on non-addressable systems. Check that during the fire condition all important functions operate (sounders, door closers etc.).

Anyone who has a business where it is going to cost them a considerable amount of money to shut-down operations really needs to have a fairly cast-iron agreement with a company who they can rely on to quickly ascertain the reason for a fault condition and be able to rectify it immediately, where possible.

When I provided such a service to Local Authorities our contract was for attendance within 4 hours. Our average attendance time was within 1 hour. In a 16 year period, I can only remember a couple of times where we had to leave them with a non-functioning system overnight. I don't think our service was much different to what our competitors could provide.

A quick attendance and repair service is not impossible, if you choose the right company. It is unlikely to be a one-man band.
« Last Edit: November 23, 2012, 02:21:42 PM by Wiz »

Offline lancsfirepro

  • Full Member
  • ***
  • Posts: 175
Re: Your opinions please - fire alarm system offline
« Reply #6 on: November 23, 2012, 02:26:21 PM »
Let's think about this another way.  Say the landlord had been operating for a number of years and didn't have a fire alarm system protecting the escape route.  Your visiting fire officer turns up on spec and after the sharp intake of breath says you need a fire alarm system and FRA etc... The enforcement notice would allow a period of time to put those measures in place; you can't expect an instant rectification.  He wouldn't normally insist that the residents were removed from the building until the alarm was installed.  Equally you must accept that from time to time things go wrong and they take time to fix.  In your example the fix is next day so you've got to ask the question "is that reasonable?"  In the grand scheme of things I would suggest that it was.

Midland Retty

  • Guest
Re: Your opinions please - fire alarm system offline
« Reply #7 on: November 23, 2012, 02:48:29 PM »
Thanks Wiz and Lancs

Wiz, sticking with my HMo for a moment. AFD in each bedsit is critical, because if a detector isn't working in a bedsit and a fire occurs and spreads, the first we would know about it is when smoke hits a detector in the communal areas. By that time the MOE is compromised. How do we check those detectors if the tenants are out and landlord or keyholder isn't available? Do we just assume the system may be ok if say the communal detectors are tested it will probably be ok? And furthermore who's job is to go round testing anyway? Is it an enforcing officer, a fire consultant? or fire alarm engineer? If so I'll need to be carrying ladders and test equipment in my car from now on! (sorry I don't wish to be confrontational)

Lancs it may not be an enforcement notice the fire authority issues, if it is a sleeping risk you will probably find prohibition notices will be issued in the first instance

Offline Fishy

  • Hero Member
  • *****
  • Posts: 777
Re: Your opinions please - fire alarm system offline
« Reply #8 on: November 23, 2012, 03:07:24 PM »
Let's think about this another way.  Say the landlord had been operating for a number of years and didn't have a fire alarm system protecting the escape route.  Your visiting fire officer turns up on spec and after the sharp intake of breath says you need a fire alarm system and FRA etc... The enforcement notice would allow a period of time to put those measures in place; you can't expect an instant rectification.  He wouldn't normally insist that the residents were removed from the building until the alarm was installed.  Equally you must accept that from time to time things go wrong and they take time to fix.  In your example the fix is next day so you've got to ask the question "is that reasonable?"  In the grand scheme of things I would suggest that it was.

...but not having kit is very different from having kit & not maintaining it properly!  The former might be understandable, but there is really never a valid excuse for the latter.

I really don’t think that I could argue that the arrangements that you describe comply with Regulation 17 of the RR(FS)O.  The recommendations in BS 5839-1 represent the acknowledged ‘good practice’ methodology for managing faults & reactive maintenance on fire detection and alarm systems.  They allow that 'instant rectification' isn't usually achievable, but they do recommend rapid attendance & attention by a competent engineer.

If the RP hasn’t put in place a means of maintenance that either complies with the BS, or that they can demonstrate is equivalently safe, it would be hard to see how it could be argued that this complies with the Law.

Offline lancsfirepro

  • Full Member
  • ***
  • Posts: 175
Re: Your opinions please - fire alarm system offline
« Reply #9 on: November 23, 2012, 03:15:08 PM »
Lancs it may not be an enforcement notice the fire authority issues, if it is a sleeping risk you will probably find prohibition notices will be issued in the first instance
Not in my experience they don't - especially if there are residents already in there.  Have a look at the CFOA Register for HMO's, you'll see it's littered with enforcement notices citing section 13.  (Granted some may refer to extinguishers but I find it's usually alarm issues they come unstuck on of the two.)

Offline Wiz

  • Hero Member
  • *****
  • Posts: 1591
Re: Your opinions please - fire alarm system offline
« Reply #10 on: November 23, 2012, 05:15:31 PM »

.....Wiz, sticking with my HMo for a moment. AFD in each bedsit is critical, because if a detector isn't working in a bedsit and a fire occurs and spreads, the first we would know about it is when smoke hits a detector in the communal areas. By that time the MOE is compromised. How do we check those detectors if the tenants are out and landlord or keyholder isn't available? Do we just assume the system may be ok if say the communal detectors are tested it will probably be ok? And furthermore who's job is to go round testing anyway? Is it an enforcing officer, a fire consultant? or fire alarm engineer? If so I'll need to be carrying ladders and test equipment in my car from now on! (sorry I don't wish to be confrontational)......



M.M., obviously you are concerned by this problem. I believe the level of concern could be modified by the results of some simple testing of the system.

It is the case that many panels, especially non-addressable, indicate only general purpose fault warnings and don't give enough information about the type and extent of the problems caused by the fault. Carrying out simple basic testing of what the fire alarm system is supposed to do will allow us to assess if the problem is extremely serious (nothing works!) or probably far less serious (the fault does not appear to have any current affect on the workings of the system!).

From the results of the test we can probably also work out if the extent of the fault is limited to specific areas etc. Obviously the more we test, if access etc. is available, the better our assessment of the seriousness of the problem can be, and also what steps the responsible person probably has to take to ensure the continued saftey of the occupants of the building.

Simple testing probably only requires a can of test smoke, a mcp test key and working eyes and ears, to be carried out effectively. We all know what a fire alarm system should be capable of doing, so it isn't that difficult to carry out basic tests of its most important functions.

Obviously the fault still needs investigating and rectifying asap. I wouldn't be happy with people sleeping in a building with a fire alarm system with a 'fault' on it without suitable fire detection patrols AND a fully working fire alarm warning sounder system.




Midland Retty

  • Guest
Re: Your opinions please - fire alarm system offline
« Reply #11 on: November 23, 2012, 05:29:55 PM »
Thanks for your detailed reply Wiz.

I can see exactly where you are coming from, and I agree its a useful process to follow

The major problem however is even if i did have my key and my can of smoke, often the tenants are unaware of the code to reset the system, or the key for the panel has gone missing or is with landlord!

Furthermore how many of us non fire alarm engineer types routinely carry ladders with us to access high detectors!

The amount of times I've stood in a HMO with a very simple fire alarm panel showing fault, and not having and any means of knowing what that fault is, nor access to all areas to determine if the system works.

I would argue that unless they are a qualified fire alarm engineer the layman could not assume a fire alarm system was working unless they were able to test every last detector, and MCP.

It goes back to the fundemental question would any of you accept a premises containing sleeping risk to have its fire alarm off line with unknown fault overnight, to await inspection by an alarm engineer next day?

Or imagine fire alarm engineer has attended but is unable to fix same day due to obtaining parts? What is reasonable?

Im often accussed that by assuming the worst I'm being 'over the top'.
« Last Edit: November 23, 2012, 05:44:07 PM by The Manic Midlander »

Offline Clevelandfire 3

  • Hero Member
  • *****
  • Posts: 566
Re: Your opinions please - fire alarm system offline
« Reply #12 on: November 23, 2012, 06:56:22 PM »
always air on the side of caution. some people will tell you your being ott until something happens and someone is hurt. then those same people will be asking why you did nothing. if temp measures cant be put in place my advice is to call your local fire brigade and have them dispatch their on call fire safety officer to deal because ultimately the premises will probably need to be prohibited.

Offline Wiz

  • Hero Member
  • *****
  • Posts: 1591
Re: Your opinions please - fire alarm system offline
« Reply #13 on: November 26, 2012, 10:34:07 AM »


It goes back to the fundemental question would any of you accept a premises containing sleeping risk to have its fire alarm off line with unknown fault overnight, to await inspection by an alarm engineer next day?




I wouldn't advise a Responsible Person that it was an acceptable risk.

Midland Retty

  • Guest
Re: Your opinions please - fire alarm system offline
« Reply #14 on: November 26, 2012, 04:18:47 PM »
Much obliged Wiz, just needed someone else to say it. I don't think I'm being OTT but sometimes you just need to be re-assured!