Author Topic: Shirley Towers Final Report  (Read 9429 times)

Offline William 29

  • Hero Member
  • *****
  • Posts: 581
    • http://www.tfsltd.net
Shirley Towers Final Report
« on: April 18, 2013, 03:47:06 PM »
http://www.hantsfire.gov.uk/jamesandalan

Very interesting but tragic, sad reading. Let’s hope lessons have been learnt and the recommendations are implemented.

Offline colin todd

  • Hero Member
  • *****
  • Posts: 3473
  • Civilianize enforcement -you know it makes sense.
    • http://www.cstodd.co.uk
Re: Shirley Towers Final Report
« Reply #1 on: April 21, 2013, 06:21:59 PM »
While people keep correctly quoting BS 5839-1: 2002 as the source of a requirement for fire alarm cables not to be supported by plastic clips, it was, in effect, necessary for compliance with the 1988 code.  It is a popular misconception that concerns over plastic clips to support these cables is a relatively recent requirement. It is not. The system at Harrow Court should not have had the cables supported by plastic.
Colin Todd, C S Todd & Associates