Fire Door Hinges
« on: February 04, 2014, 10:51:06 AM »
Hi folks,

Has anyone come across the product in the link below before?

http://www.moderndoorclosers.co.uk/fire-door-hinge-closers.html

A number of our surveyors are wanting to specify it for fitting on flat entrance doors as it overxomes a problem that some older people have in opening their front doors, when they are fitted with self-closing devices.

If you have used it anywhere I'd really appreciate knowing if you felt it was effective.

Regards,

Geoff

Offline nearlythere

  • Hero Member
  • *****
  • Posts: 4351
Re: Fire Door Hinges
« Reply #1 on: February 04, 2014, 11:52:14 AM »
I'm sure you are aware Geoff they do not comply with BS EN 1154 - Door Closers. Their only claim is that it complies with BS476 Part 22 in that it withstood fire for an hour not that it acted as a BS EN 1154 device with regards to self closing.

We're not Brazil we're Northern Ireland.

Offline John Webb

  • Hero Member
  • *****
  • Posts: 838
Re: Fire Door Hinges
« Reply #2 on: February 04, 2014, 08:29:18 PM »
Interesting item - I'm a bit concerned that they operate from mobile phones and don't give a postal address, however..... But I may be doing them an injustice?
John Webb
Consultant on Fire Safety, Diocese of St Albans
(Views expressed are my own)

Offline wee brian

  • Administrator
  • Hero Member
  • *****
  • Posts: 2424
Re: Fire Door Hinges
« Reply #3 on: February 05, 2014, 12:55:05 PM »
The EC flag/logo is a bit suspect too - are they just confirming that they live somewhere in Europe?

Has anybody seen these things in action?

Offline nearlythere

  • Hero Member
  • *****
  • Posts: 4351
Re: Fire Door Hinges
« Reply #4 on: February 05, 2014, 01:42:10 PM »
There is nowhere on the site that they claim it is suitable for a SC fire door which is fine. But the picture of the doors in the Features and Benefits page seem to have what look like Fire Door keep Closed signs. Perhaps they are acceptable elsewhere in the world?
We're not Brazil we're Northern Ireland.

Offline nearlythere

  • Hero Member
  • *****
  • Posts: 4351
Re: Fire Door Hinges
« Reply #5 on: February 05, 2014, 01:49:57 PM »

In the home page it is presented as an alternative to an overhead self closing device but no mention of fire doors that I can see.

So far buyer beware.
« Last Edit: February 05, 2014, 01:52:53 PM by nearlythere »
We're not Brazil we're Northern Ireland.

Offline Davo

  • Hero Member
  • *****
  • Posts: 1144
Re: Fire Door Hinges
« Reply #6 on: February 06, 2014, 08:41:32 PM »
Geoff

why would you want a closer on the front door? not sure of the context.

what about the latest Perko fittings?

davo

Offline Geoff

  • Jr. Member
  • **
  • Posts: 79
Re: Fire Door Hinges
« Reply #7 on: February 14, 2014, 07:10:40 PM »
Apologies I should have said that the doors are flat entrance doors in retirement and extra care schemes. The issue is that many residents struggle with any form of resistance provided by door closures. We also use free swing devices as well but the same problem occurs when they activate, some can't open the door.

So the surveyors are always looking for an alternative!

This looks to be a good solution but like others have mentioned they are lacking in a bit of provenance and that is why I consulted you wize chaps!


« Last Edit: February 14, 2014, 07:12:47 PM by Geoff »

Offline Tadees

  • Full Member
  • ***
  • Posts: 122
Re: Fire Door Hinges
« Reply #8 on: March 01, 2015, 02:24:39 PM »
I'm sure you are aware Geoff they do not comply with BS EN 1154 - Door Closers. Their only claim is that it complies with BS476 Part 22 in that it withstood fire for an hour not that it acted as a BS EN 1154 device with regards to self closing.



What's so special about a BS EN 1154 closer that can't be achieved by a BS476 Part 22 compliant closer?  If it can withstand fire and it shuts the door in to its rebate from any angle, what's the problem?  Not trying to be funny.  Just a genuine question.
Some people are like clouds. When they disappear it's a brighter day.

Offline Messy

  • Sr. Member
  • ****
  • Posts: 343
Re: Fire Door Hinges
« Reply #9 on: March 01, 2015, 04:49:45 PM »
Interesting item - I'm a bit concerned that they operate from mobile phones and don't give a postal address, however..... But I may be doing them an injustice?

The registered address of Modern Door Closers is: 9 Wick Close, Bognor Regis PO22 8QE (a small cul-de-sac of small bungalows)

The same address as Rye International Corporation (who are listed as a transport & haulage company)

Neither have a website

(A West Sussex Arthur Daley perhaps??)

Offline Tom Sutton

  • Hero Member
  • *****
  • Posts: 2287
Re: Fire Door Hinges
« Reply #10 on: March 01, 2015, 07:55:51 PM »

What's so special about a BS EN 1154 closer that can't be achieved by a BS476 Part 22 compliant closer?  If it can withstand fire and it shuts the door in to its rebate from any angle, what's the problem?  Not trying to be funny.  Just a genuine question.

Because the standard for self closers is BS EN 1154 and it should should be also meet BS EN 1935 for hinges but BS 476 pt 22 is irrelevant, unless the method of installation may affect the fire resistance of the fire door.

If you only wish to close the door why not use a single chain perko but I would not recommend it for fire doors.
« Last Edit: March 01, 2015, 07:58:46 PM by Tom Sutton »
All my responses only apply to England and Wales and they are an overview of the subject, hopefully it will point you in the right direction and always treat with caution.

Offline AnthonyB

  • Firenet Extinguisher Expert
  • Global Moderator
  • Hero Member
  • *****
  • Posts: 2480
    • http://www.firewizard.co.uk
Re: Fire Door Hinges
« Reply #11 on: March 02, 2015, 03:53:08 PM »
I remember reading in some old guidance that only double chain perkos were suitable for fire doors and back in 1993 (or even 1986, but I don't have a first edition) the Guild of Architectural Ironmongers guide to ironmongery on timber fire doors cautioned against the use of Concealed Non Check Jamb Morticed Door closers (the generic name for Perkos!)

The use of a spring hinge as part of the device in the link would have precluded from use under the old '93 guidance as well
Anthony Buck
Owner & Fire Safety Consultant at Fire Wizard


Extinguisher/Fire History Enthusiast

Fire Extinguisher Facebook Group:
http://www.facebook.com/group.php?gid=65...415&ref=ts
http://www.youtube.com/user/contactacb
https://uk.linkedin.com/in/anthony-buck-36

Offline Tom Sutton

  • Hero Member
  • *****
  • Posts: 2287
Re: Fire Door Hinges
« Reply #12 on: March 02, 2015, 08:04:12 PM »
There is also no indication that they are CE marked and if they are who did the assessment?
All my responses only apply to England and Wales and they are an overview of the subject, hopefully it will point you in the right direction and always treat with caution.

Offline wee brian

  • Administrator
  • Hero Member
  • *****
  • Posts: 2424
Re: Fire Door Hinges
« Reply #13 on: March 03, 2015, 10:14:28 AM »
There's a BBA Logo. The BBA certificate (if it exists) will (should) list all that's been tested/certified etc.

Offline Tom Sutton

  • Hero Member
  • *****
  • Posts: 2287
Re: Fire Door Hinges
« Reply #14 on: March 03, 2015, 02:34:04 PM »
WB I have tried to find it on their site, but it is a nightmare the system they use is crap.
All my responses only apply to England and Wales and they are an overview of the subject, hopefully it will point you in the right direction and always treat with caution.