Author Topic: Flat front door glazing  (Read 13802 times)

Offline AJAY

  • Newbie
  • *
  • Posts: 9
Flat front door glazing
« on: August 19, 2014, 12:01:29 PM »
Morning all,

I have recently visited a converted block of flats which is a listed building.

It appears that the flat front doors have the original stained glass in the door panels and also above the doors. This unfortunately is not fire resisting enough to protect the means of escape corridors/stairwell as their is no lobby and the flats open directly on to the corridors.

What would be an acceptable solution to upgrading the glazing?
Is there anything on the market like a coating?
Would the doors need fully upgrading or the glazed bits boarding over?

There is a automatic fire alarm system fitted - call points & AFD to L2.   

Any suggestions would be appreciated!

Offline nearlythere

  • Hero Member
  • *****
  • Posts: 4351
Re: Flat front door glazing
« Reply #1 on: August 19, 2014, 12:13:38 PM »
Is there room in the frames to double up the existing glass with georgian wire or copper strip or insulated if you prefer?
We're not Brazil we're Northern Ireland.

Offline AJAY

  • Newbie
  • *
  • Posts: 9
Re: Flat front door glazing
« Reply #2 on: August 19, 2014, 12:53:58 PM »
Hi Nearlythere,

Difficult to say, as the glazing appears to be in bevelled frames. Not sure if there would be enough space to fit GW panels

Offline AnthonyB

  • Firenet Extinguisher Expert
  • Global Moderator
  • Hero Member
  • *****
  • Posts: 2480
    • http://www.firewizard.co.uk
Re: Flat front door glazing
« Reply #3 on: August 19, 2014, 09:59:48 PM »
The category of fire alarm is suggestive of someone's previous solution to this issue being to move to full evacuate rather than stay put....
Anthony Buck
Owner & Fire Safety Consultant at Fire Wizard


Extinguisher/Fire History Enthusiast

Fire Extinguisher Facebook Group:
http://www.facebook.com/group.php?gid=65...415&ref=ts
http://www.youtube.com/user/contactacb
https://uk.linkedin.com/in/anthony-buck-36

Offline Auntie LIn

  • Full Member
  • ***
  • Posts: 107
Re: Flat front door glazing
« Reply #4 on: August 20, 2014, 09:31:57 PM »
You might consider applying an overlay of gwpp on the internal face.   The detailing would need careful consideration and it wouldn't be the prettiest solution but it might do the job.

Offline Davo

  • Hero Member
  • *****
  • Posts: 1144
Re: Flat front door glazing
« Reply #5 on: August 21, 2014, 10:10:05 PM »
Aunty Lin is spot on, we did this at my old HQ back in the eighties, all interested parties found acceptable as you could still see the stained glass

davo

Offline Fishy

  • Hero Member
  • *****
  • Posts: 777
Re: Flat front door glazing
« Reply #6 on: October 28, 2014, 07:55:48 AM »
If you put non-insulating F/R glass on the fire risk face, then it'll overheat and fail early (the non-F/R glass insulates it).   I think you might find that the recommended/tested upgrading detail for glazing is to put the F/R glazing system on the non-risk face (counter-intuitive perhaps but that's what my experience has revealed).  Alternatively you can use an EI glass on the risk face, if there's room to fit it.

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: Flat front door glazing
« Reply #7 on: October 28, 2014, 11:23:14 PM »
Crikey Fishy I would never have expected that! Was your experience of the performance of non insulating glass founded in testing  or experience of observing real fires?

Offline Fishy

  • Hero Member
  • *****
  • Posts: 777
Re: Flat front door glazing
« Reply #8 on: October 29, 2014, 10:30:43 AM »
Testing and research.  The non-fr glass doesn't allow the FR glass to lose heat like it is designed to, so it (and its glazing system) can overheat.  GWPP is particularly prone to early failure if you insulate it.  Also, if the F/R glass is on the risk face and the secondary glazing detail uses timber between the panes then it cooks the timber which can ignite, negating the protection that the f/r glass provides.  Not an issue for the EI insulating glasses, but they are much thicker, of course.
« Last Edit: December 24, 2014, 10:07:48 AM by Fishy »

Offline nearlythere

  • Hero Member
  • *****
  • Posts: 4351
Re: Flat front door glazing
« Reply #9 on: October 30, 2014, 02:37:39 PM »
Testing and research.  GWPP is particularly prone to early failure if you insulate it.  Also, if the F/R glass is on the risk face and the secondary glazing detail uses timber between the panes then it can ignite, negating the protection that the f/r glass provides.  Not an issue for the EI insulating glasses, but they are much thicker, of course.

Very interesting.
We're not Brazil we're Northern Ireland.

Offline Daffodil

  • Newbie
  • *
  • Posts: 22
Re: Flat front door glazing
« Reply #10 on: November 18, 2014, 12:28:33 PM »
I am told that there is a product caled XYZ from envirograf that is a laquer and a film that can upgrade glass.  I have never seen it applied so I do not know how good it is and if the frames of the exising windows would suffice.

Offline Auntie LIn

  • Full Member
  • ***
  • Posts: 107
Re: Flat front door glazing
« Reply #11 on: November 20, 2014, 01:33:48 PM »
Upgrade it from what to what?   Has it been tested in the way in which it is proposed to be used?   Has the correct test procedure been used?   All questions that you should want answered about any material which claims to upgrade anything.

Offline colin todd

  • Hero Member
  • *****
  • Posts: 3473
  • Civilianize enforcement -you know it makes sense.
    • http://www.cstodd.co.uk
Re: Flat front door glazing
« Reply #12 on: November 22, 2014, 06:24:42 PM »
You are becoming old and cynical Lin. Soon you will be smelling Dave's breath when he says he was late because he went to visit an ill relative.

Like Ajay, I too recently visited a block of flats that was a conversion. I took afternoon tea with my elderly aunt.  Then I went home.
Colin Todd, C S Todd & Associates

Offline Firescot

  • Newbie
  • *
  • Posts: 8
Re: Flat front door glazing
« Reply #13 on: November 22, 2014, 11:35:15 PM »
Could you not fit an inner fire resistant lobby and leave the original doors the way they are?