Author Topic: Hospital Streets  (Read 12986 times)

Offline lingmoor

  • Sr. Member
  • ****
  • Posts: 264
Hospital Streets
« on: September 04, 2014, 03:21:19 PM »
This section usually has tumbleweed blowing through it but anyway...

HTM 05-02 page 24 says that Hospital Streets should contain 'no other accomodation' other that sanitary accomodation and theres an explanatory diagram on page 25

The diagram depicts a Hospital Street with large units off it that are marked 'Hospital Accomodation'

I can only assume that these are depicting Wards/Outpatients etc...

so does this mean that the  'no other accomodation other than sanitory accom.' bit means no other accomodation other than  wards/outpatients are allowed apart from sanitory accom?

for example no admin offices

check out pages 24 and 25

https://www.gov.uk/government/uploads/system/uploads/attachment_data/file/308846/HTM_05-02_2014.pdf


Maybe Colin Newman can shed a bit of light?



Offline AnthonyB

  • Firenet Extinguisher Expert
  • Global Moderator
  • Hero Member
  • *****
  • Posts: 2480
    • http://www.firewizard.co.uk
Re: Hospital Streets
« Reply #1 on: September 04, 2014, 08:49:06 PM »
The 'Hospital Accommodation' isn't contained in the street, but is in separate adjacent full fire compartments of 60 minutes.

It means (in my interpretation) nothing should be contained within the fire compartment that forms the street other than toilets - so for example you couldn't have a cleaners cupboard, linen store, within the area. It would all have to be within  in a separate compartment off the street
Anthony Buck
Owner & Fire Safety Consultant at Fire Wizard


Extinguisher/Fire History Enthusiast

Fire Extinguisher Facebook Group:
http://www.facebook.com/group.php?gid=65...415&ref=ts
http://www.youtube.com/user/contactacb
https://uk.linkedin.com/in/anthony-buck-36

Offline lingmoor

  • Sr. Member
  • ****
  • Posts: 264
Re: Hospital Streets
« Reply #2 on: September 08, 2014, 09:49:42 AM »
Thanks Anthony... now you've said that, it is something I should have interpretated myself the same way....I was looking at the wards that are contained off the Street, but as you correctly point out they are a seperate compartment

Can't see the woods for the trees

Offline Colin Newman

  • Full Member
  • ***
  • Posts: 114
    • Healthfire
Re: Hospital Streets
« Reply #3 on: September 10, 2014, 02:34:33 AM »
Anthony is correct.  Only sanitary accommodation is permitted within the hospital street, all other accommodation should be separated by a minimum of 60 minutes fire resisting construction. 

Just one thing to note (which usually gives some problems), 3.38a prohibits entrances from the hospital street to adjoining compartments from the same section of the hospital street that provides entrances to stairs or lifts. i.e. You cannot have a cleaner's cupboard accessed from the same section of a hospital street as a stair or lift, even if the cupboard is separated by 60 minutes FR.

Offline lingmoor

  • Sr. Member
  • ****
  • Posts: 264
Re: Hospital Streets
« Reply #4 on: September 11, 2014, 09:34:50 AM »
Thank you Colin