Author Topic: Stairway enclosures without detection  (Read 11763 times)

Offline nearlythere

  • Hero Member
  • *****
  • Posts: 4351
Stairway enclosures without detection
« on: October 07, 2014, 09:18:11 PM »
What do we think of this folks.

10 storey building with two stairway enclosures. On has final exit and the other (main stairway) exit via a lift lobby and reception.
Single point of access to each stairway at each level.

No service shafts in either stairway.

Main Stairway - Completely sterile and no detection within stairway but detection in adjacent room which is lift lobby at all levels.
Alternative Stairway - Also sterile with no detection in enclosure but has protected lobby approach on each level from open plan office area containing detection.

So I'm thinking - what's the problem?
We're not Brazil we're Northern Ireland.

Offline Davo

  • Hero Member
  • *****
  • Posts: 1144
Re: Stairway enclosures without detection
« Reply #1 on: October 07, 2014, 09:57:01 PM »
Nearlythere

Liklihood of remaining sterile? How is the security? Arson?

davo

Offline nearlythere

  • Hero Member
  • *****
  • Posts: 4351
Re: Stairway enclosures without detection
« Reply #2 on: October 08, 2014, 07:34:16 AM »
Nearlythere

Liklihood of remaining sterile? How is the security? Arson?

davo

Very likely to remain sterile & arson? How do you deal with a single stairway condition?

Security staff at main entrance. Rear escape stairway secure from outside access.

We're not Brazil we're Northern Ireland.

Offline Mr. P

  • Hero Member
  • *****
  • Posts: 685
Re: Stairway enclosures without detection
« Reply #3 on: October 08, 2014, 10:24:41 AM »
Suitable/reasonable control/management, 2 way escape. Are stairs sized for number of occupants?

Offline nearlythere

  • Hero Member
  • *****
  • Posts: 4351
Re: Stairway enclosures without detection
« Reply #4 on: October 08, 2014, 09:13:06 PM »

So I'm thinking - what's the problem?


Dunno.  What is it?
That what I'm asking? Lots of opinions would make good chat. Is that not one of the points of the forum? Debate?
We're not Brazil we're Northern Ireland.

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: Stairway enclosures without detection
« Reply #5 on: October 08, 2014, 10:28:35 PM »
What is the building used for NT? Single or multi occ?

Offline nearlythere

  • Hero Member
  • *****
  • Posts: 4351
Re: Stairway enclosures without detection
« Reply #6 on: October 09, 2014, 06:44:57 AM »
What is the building used for NT? Single or multi occ?
Single.
We're not Brazil we're Northern Ireland.

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: Stairway enclosures without detection
« Reply #7 on: October 09, 2014, 05:34:19 PM »
What's it used for NT? Offices? Hotel? Flats? Hospital? Firework factory?

Offline Clevelandfire 3

  • Hero Member
  • *****
  • Posts: 566
Re: Stairway enclosures without detection
« Reply #8 on: October 09, 2014, 05:49:01 PM »
No problem to me. Theres 2 staircases. We always say you will only have one fire. people can turn their back and go the other way. Doesn't matter if both staircases become poorly managed so long as theyre both separated. 

Offline nearlythere

  • Hero Member
  • *****
  • Posts: 4351
Re: Stairway enclosures without detection
« Reply #9 on: October 09, 2014, 09:24:41 PM »
What's it used for NT? Offices? Hotel? Flats? Hospital? Firework factory?
Office.
We're not Brazil we're Northern Ireland.

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: Stairway enclosures without detection
« Reply #10 on: October 10, 2014, 07:06:33 AM »
Presumably at least one of the staircases is a firefighting shaft with a firefighting lobby due to the height of the building........ I  suggest that if building it today you would follow bs5839 and incorporate detection in accordance with the Relevant  L category, but if encountering it on an FRA as an existing building it might be difficult to justify the cost / benefit of a retro fit of detection especially where the staircase(s) are firefighting stairs with firefighting lobbies in a single occupier (or well managed multi occ ) building.

Offline colin todd

  • Hero Member
  • *****
  • Posts: 3473
  • Civilianize enforcement -you know it makes sense.
    • http://www.cstodd.co.uk
Re: Stairway enclosures without detection
« Reply #11 on: October 13, 2014, 11:56:24 PM »
Why would you need afd in an office building.
Colin Todd, C S Todd & Associates

Offline Davo

  • Hero Member
  • *****
  • Posts: 1144
Re: Stairway enclosures without detection
« Reply #12 on: October 14, 2014, 07:30:54 PM »
How long have you got...........

davo

Offline colin todd

  • Hero Member
  • *****
  • Posts: 3473
  • Civilianize enforcement -you know it makes sense.
    • http://www.cstodd.co.uk
Re: Stairway enclosures without detection
« Reply #13 on: October 15, 2014, 10:17:52 PM »
I have infinite patience. It comes from dealing with the English FRS.
Colin Todd, C S Todd & Associates

Offline Wiz

  • Hero Member
  • *****
  • Posts: 1591
Re: Stairway enclosures without detection
« Reply #14 on: October 16, 2014, 10:00:05 AM »
Why would you need afd in an office building.

just to quote a few from Table A.1 of BS5839-1 which could apply to office buildings:

a) Buildings in which other fire precautions, such as means of escape, depart from recognized guidance.

b) Buildings with "inner rooms", from which escape is possible only passing through another ("access") room, where there is inadequate vision between the inner room and the access room.

c) Buildings in which automatic fire detection is required to operate other fire protection systems (e.g. magnetic door holders)

d) Situations in which fire could readily spread from an unoccupied area and prejudice means of escape from occupied areas.

e) Any building in which automatic detection is provided as a requirement of a property insurers or to attract an insurance premium discount.

I'm sure there must be other reasons which could apply.

I haven't got a clue who was involved in creating BS5839-1, but I imagine they would know what they are doing. They are my heroes and I look up to them!  ;)