Taken from the rule 43 letter following the INQUEST INTO THE DEATHS OF ALAN BANNON AND JAMES SHEARS
Granted these two gentlemen were fire-fighters. However a member of the public died at Harrow Court along with 2 fire fighters.
It is recommended that all FRSs and social housing providers consider the Rule 43 recommendations made by HM Coroner for Hertfordshire following the inquest into fire-fighter fatalities at Harrow Court in particular
Recommendation 8 made by the FBU which is here repeated for ease of reference: That SBC should remove all the surface mounted plastic trunking/conduit used to protect and support the Fire Alarm and Automatic Fire Detection System in the Common Areas of all their premises, and replace them with a method of cable support which as a minimum conforms to BS 5839- Part 1 : 2002; clause 26.2 (f:);
Methods of cable support should be such that circuit integrity will not be reduced below that afforded by the cable used, and should withstand a similar temperature and duration to that of the cable, while maintaining adequate support. Note 7. In effect, this recommendation precludes the use of plastic cable clips, cable ties or trunking, where these products are the sole means of cable support. 6 It is recommended that Building Regulations are amended to ensure that all cables, not just fire alarm cables, are supported by fire-resistant cable supports. This could be achieved by an amendment to BS 7671 (2008) Institute of Electrical Engineers Wiring Regulations.