With the self testing stuff it usually falls into various types, the ones I've encountered:
- self contained bulkheads with their own testing circuit & status indicators
- self contained bulkheads with their own testing circuit linked into a central control and indicating system
- slave LED's powered by a loop with a central PSU, control and indicating system
With the central indicator type panels I normally ask for a monthly interrogation of the system readout to identify any faults and a record held to prove it's been looked at and say 'all OK' or 'faults to units 12,34, etc' - thus in the spirit of the testing for traditional fittings.
I also advise that the fittings be walked monthly to identify issues that the testing system cannot - e,g, discoloured or damaged diffusers, etc.
Where the fittings are self testing but not centrally monitored, then they need to be walked not just for the physical damage factors, but to check the status LEDs for any showing a fault.
Obviously it's impractical to try and record an annual test as it's being staggered throughout the year automatically.
The control and indicating equipment requires suitable PPM as well.