Author Topic: Fire Equipment Required in Fully Enclosed Car Park  (Read 15180 times)

Offline Suttonfire

  • Full Member
  • ***
  • Posts: 130
Fire Equipment Required in Fully Enclosed Car Park
« on: July 19, 2015, 11:22:03 AM »
Hi All,

I'm doing some research on the above and as part of this I would appreciate some views on what you would typically expect to find installed in terms of fire protection equipment (subject to risk assessment) installed in a fully enclosed car park, i.e. type and grade of detection and warning, mechanical smoke extraction, sprinklers/other extinguishing equipment etc

thanks

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: Fire Equipment Required in Fully Enclosed Car Park
« Reply #1 on: July 19, 2015, 05:14:35 PM »
I suppose there are obvious questions like is it above or below ground, how big is it and is it in an area subject to local enactments? Is it part of a building complex or a stand alone car park?

Offline Dinnertime Dave

  • Hero Member
  • *****
  • Posts: 819
Re: Fire Equipment Required in Fully Enclosed Car Park
« Reply #2 on: July 19, 2015, 05:42:41 PM »

The submissions I've seen seem to rely on the enclosed car park being no worse than a code (ADB) compliant one. This was done via CFD modelling.

Surprisingly, the model showed it to be no worse - even after pointing out the fire sizes they used were incorrect.

Offline Tom Sutton

  • Hero Member
  • *****
  • Posts: 2287
Re: Fire Equipment Required in Fully Enclosed Car Park
« Reply #3 on: July 19, 2015, 05:46:51 PM »
Goole for "fire safety in enclosed car park" you will get lots of stuff, like http://www.gov.scot/Resource/0041/00418073.pdf check out the scope.
All my responses only apply to England and Wales and they are an overview of the subject, hopefully it will point you in the right direction and always treat with caution.

Offline Suttonfire

  • Full Member
  • ***
  • Posts: 130
Re: Fire Equipment Required in Fully Enclosed Car Park
« Reply #4 on: July 19, 2015, 09:04:23 PM »
I have found lots of guidance etc to read through thanks.

The car park in question is a large warehouse due to be converted into an enclosed car park.

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: Fire Equipment Required in Fully Enclosed Car Park
« Reply #5 on: July 19, 2015, 10:04:11 PM »
In such situations very little is probably needed. Often such conversions are for car parking at airports etc where parking is long term so persons at risk are very low. Roof is high so for life safety some relaxations may be appropriate for travel distances. Video surveillance may suffice for detection. Consider location, I think some places may still have some local enactments in place for petrol aggregation, that went over and above dsear. I would be pleased to be corrected if wrong on this. The biggest issue may be property protection as if high density parking they ram them in with no space at all between vehicles. I had a job like this at an airport, that was complicated by the fact that half the hangar was still used for aircraft with an aggregate value of many millions.

Offline Phoenix

  • Hero Member
  • *****
  • Posts: 677
  • Get a bicycle. You will not live to regret it
    • MetaSolutions (Fire Safety Engineering) Ltd.
Re: Fire Equipment Required in Fully Enclosed Car Park
« Reply #6 on: July 20, 2015, 08:47:26 AM »
I would expect to see some facilities for cross ventilation, both every day ventilation (for Part F) and for fire conditions (Part B).  The floor should be impervious to petrol.  Satisfactory means of escape of course, but ignore the occupancy factor suggested in ADB unless you have good reason to think that such an onerous figure might be accurate.

Offline Dinnertime Dave

  • Hero Member
  • *****
  • Posts: 819
Re: Fire Equipment Required in Fully Enclosed Car Park
« Reply #7 on: July 20, 2015, 04:17:23 PM »

Agreed Phoenix, the occupancy factors are little excessive, dealt with a MSCP with over 1200 spaces stair sizes were enormous. Came to a compromise.  As long as the car park isn't attached to a Threatre etc it is unlikely everyone will be there together. Access was difficult over 18m high.

Offline colin todd

  • Hero Member
  • *****
  • Posts: 3473
  • Civilianize enforcement -you know it makes sense.
    • http://www.cstodd.co.uk
Re: Fire Equipment Required in Fully Enclosed Car Park
« Reply #8 on: July 20, 2015, 10:28:01 PM »
Local enactments, Big Al???  What local enactments?
Colin Todd, C S Todd & Associates

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: Fire Equipment Required in Fully Enclosed Car Park
« Reply #9 on: July 21, 2015, 06:40:11 PM »
Colin at the time of posting I was not certain and did not have time to check if the The Building (Repeal of Provisions of Local Acts) Regulations 2012 repealed those provisions within local enactments covering safety of parking places. I have now checked and can confirm that these elements were repealed. However there remain, as far as I can see, some local enactments in force relating to fire, in respect of the storage of stacks of flammable materials notably timber and plastics. Unless you can advise otherwise?

Offline colin todd

  • Hero Member
  • *****
  • Posts: 3473
  • Civilianize enforcement -you know it makes sense.
    • http://www.cstodd.co.uk
Re: Fire Equipment Required in Fully Enclosed Car Park
« Reply #10 on: July 21, 2015, 10:17:25 PM »
Not a lot of call for stacking of timber in a car park, Big Al.  What you meant is actually oops I forgot that the relevant provisions of local acts were repealed, possibly?
Colin Todd, C S Todd & Associates

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: Fire Equipment Required in Fully Enclosed Car Park
« Reply #11 on: July 22, 2015, 09:20:58 AM »
What I meant Colin is to point out that not all local enactments were repealed in 2012 as I thought  you implied in your posting.

  Though off topic I thought the provisions for stacks of timber and plastic particularly relevant in view of yesterdays pallet fire in Enfield.

http://www.london24.com/news/enfield_fire_huge_blaze_sending_up_smoke_visible_all_over_london_1_4161596

Offline wee brian

  • Administrator
  • Hero Member
  • *****
  • Posts: 2425
Re: Fire Equipment Required in Fully Enclosed Car Park
« Reply #12 on: July 22, 2015, 02:01:50 PM »
I think the stack stuff is still extant. The Building (Repeal of Provisions of Local Acts) Regulations 2012 wouldn't have repealed them as they dont relate to buildings. The Fire safety order repealed or modified a lot of local act provisions but I dont think it did for the provisions releating to stacks.

Offline colin todd

  • Hero Member
  • *****
  • Posts: 3473
  • Civilianize enforcement -you know it makes sense.
    • http://www.cstodd.co.uk
Re: Fire Equipment Required in Fully Enclosed Car Park
« Reply #13 on: July 25, 2015, 12:02:39 AM »
The stacks of stuff on stacks still exists as far as I am aware.
Colin Todd, C S Todd & Associates

Offline Suttonfire

  • Full Member
  • ***
  • Posts: 130
Re: Fire Equipment Required in Fully Enclosed Car Park
« Reply #14 on: January 11, 2016, 11:20:33 AM »
Interestingly, since this discussion I have now completed fire risk assessments on 2 public open sided car parks, and my reports have been criticized by an involved contractor for not recommending that a 'fire alarm and automatic suppression system is installed'. Apparently I should have also recommended that dry riser systems are retro fitted. My assessment of the risks and understanding of current guidance did not find that any of this is ne.

I am now required to meet with the Local Fire Officer to justify my report.

I find it increasingly frustrating that you can take the time to consider all current approved guidance etc, discuss the issue with other industry professionals and base your recommendations on actual risks, and still find that 'adequacy' of your assessment is called into question by parties who do not seem to have taken all factors into consideration to the same extent (it will be interesting to see what the Fire Officer makes of it!).

Do others find this to be the case? Would any of you typically recommend the retrospective installation of the equipment mentioned above in a public open sided car park?