Author Topic: Grade A LD2 (Three Storey HMO)  (Read 6028 times)

Offline Tadees

  • Full Member
  • ***
  • Posts: 122
Grade A LD2 (Three Storey HMO)
« on: September 18, 2015, 05:23:14 PM »
It is as clear as mud in the BS, Lacors & the Sleeping Guide whether the heat detectors in the kitchen and living room of a bedsit in a 3 storey HMO should be linked to the communal system. 

Lacors clearly implies it, the BS kind of implies it (when read as a whole) and the Sleeping Guide says there is no need.  I guess it has to be determined on the basis of a FRA, but it would be nice if all guides said the same thing, or is that too difficult?
Some people are like clouds. When they disappear it's a brighter day.

Offline colin todd

  • Hero Member
  • *****
  • Posts: 3473
  • Civilianize enforcement -you know it makes sense.
    • http://www.cstodd.co.uk
Re: Grade A LD2 (Three Storey HMO)
« Reply #1 on: September 18, 2015, 11:50:27 PM »
Too difficult.
Colin Todd, C S Todd & Associates

Offline wee brian

  • Administrator
  • Hero Member
  • *****
  • Posts: 2424
Re: Grade A LD2 (Three Storey HMO)
« Reply #2 on: September 21, 2015, 01:48:31 PM »
Dont worry, the smoke detectors in adjacent rooms will probably go off first anyway :)

Offline Tom Sutton

  • Hero Member
  • *****
  • Posts: 2287
Re: Grade A LD2 (Three Storey HMO)
« Reply #3 on: September 21, 2015, 03:48:13 PM »
I think the guidance deals with different situations so it cannot be definitive it is left up to you, as a competent risk assessor, to select the best situation for each case.
All my responses only apply to England and Wales and they are an overview of the subject, hopefully it will point you in the right direction and always treat with caution.

Offline Mike Buckley

  • Hero Member
  • *****
  • Posts: 1045
Re: Grade A LD2 (Three Storey HMO)
« Reply #4 on: September 21, 2015, 04:24:42 PM »
All well and good until the EHO acting under the Housing Act starts to put his pennyworth.
The presence of those seeking the truth is infinitely to be preferred to those who think they've found it.

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: Grade A LD2 (Three Storey HMO)
« Reply #5 on: September 21, 2015, 07:17:21 PM »
If it really is a  BS 5839-6 compliant Grade A LD2  system then one would expect the detectors to be interlinked?  This is the technical standard for such an alarm system. The other guidance documents referred to are building design / risk assessment guides and as a result of the fire risk assessment it might be concluded that variations from BS 5839-6 are appropriate, in which case they should be documented as such.