Thank you for the replies. The proposal is indeed to convert the wet system to a pre action system where two detector heads need to be actuated and the bulb fractured before the mist will be produced.
I hadn't considered considering an alternative system where the fire detection system is defective - but I will now. However, I am not happy with converting it to a wet system every time the AFD goes down. The time, cost & disruption of draining the system in order to convert it back to a pre action system would not be acceptable
The staff movement from across the atrium is an early part of the phased evacuation system, where staff are moved horizontally away from the suspected fire. If the fire detection system moves to a subsequent stage, the evacuation message is changed to proceed downstairs and outside.
I haven't seen the premises yet as the preliminary work has been via drawings only, but I should know more in a fortnight or so after the 1st site visit. Thanks