The FA category, configuration is clearly given in BS5839:6:2013, do we need anything further as that seems to provide all the info for this thread? Extract below:
CT can you point us to the 45dB(A) ref please.
Fire alarms for sheltered housing schemes are now included in current fire safety guidance, BS 5839-6:2013 Fire detection and fire alarm systems for buildings ? Part6: Code of practice for the design, installation, commissioning and maintenance of fire detection and fire alarm systems in domestic properties. In general, the design of sheltered housing is very similar, or identical, to the design of purpose built flats, and each flat is an independent, fire-resisting compartment, within which a fire is expected to be contained. This facilitates a stay put policy, in which only the occupants of the flat of fire origin need to evacuate, while it is safe for other residents to remain within their own flat. However, as in general needs flats, a stay put policy is predicated on the assumption that the fire and rescue service will attend and extinguish the fire. It is also assumed that, if necessary, the fire and rescue service will instruct residents, in flats that might ultimately be affected by the fire, to evacuate. In the case of sheltered housing, residents might be slower to evacuate if required to do so and accordingly, there is a need to compensate for this by earlier attendance of the fire and rescue service.
Therefore the objectives of fire warning arrangements in sheltered housing are:
a) To alert residents of a fire within their flat to enable their early evacuation ? with a category LD3, grade D fire alarm system.
b) To alert the fire and rescue service to the fire, so facilitating early attendance while avoiding, as far as practicable, attendance to false alarms ? this can be achieved by connecting the flat fire alarm to the 2 way communications system in each flat thereby sending a signal to the scheme manager or remote alarm receiving centre.
c) Early detection of a fire in any communal facilities (such as lounges, laundries or guest bedroom) that might grow to affect common escape routes - fire alarm system for the communal areas only.
This configuration of fire alarm system reduces the number of false alarms and unrequired attendance of the fire service, causes the minimum of disruption to residents, residents can stay put and only need to evacuate if their flat is involved in fire or from the communal areas if the communal fire alarm sounds.