Table 19 BS 9999:2017
« on: January 27, 2017, 06:58:40 PM »
Guys, slowly ploughing my way through the revised standard. Just a quickie ... table 19 fire service vehicular access doesn't contain guidance on high reach appliances? Is this an omission or am I missing something??

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: Table 19 BS 9999:2017
« Reply #1 on: January 28, 2017, 11:56:23 AM »
As I have retired I have not bought a copy to check but I would suggest if it isn't there it's a serious omission in error. Fact is though pumping appliances are bigger and heavier nowadays but high rise are still  bigger and more difficult to manoeuvre.
« Last Edit: January 28, 2017, 11:59:30 AM by kurnal »

Offline Tom Sutton

  • Hero Member
  • *****
  • Posts: 2287
Re: Table 19 BS 9999:2017
« Reply #2 on: January 28, 2017, 03:10:39 PM »
Would you need a high reach appliance on building lower than 11m, (table 19) check out table 20?
All my responses only apply to England and Wales and they are an overview of the subject, hopefully it will point you in the right direction and always treat with caution.

Offline Revol

  • Jr. Member
  • **
  • Posts: 71
Re: Table 19 BS 9999:2017
« Reply #3 on: January 28, 2017, 05:25:51 PM »
Would you need a high reach appliance on building lower than 11m, (table 19) check out table 20?

Yes, you would require high reach access to a storage building as the height is measured to mean roof height.
Table 20 covers the road widths etc. Same as table 20 in ADB.

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: Table 19 BS 9999:2017
« Reply #4 on: January 28, 2017, 08:39:11 PM »
Thanks my mistake. Time to pack this game in I think as I can't keep up to date any longer.

Offline Tom Sutton

  • Hero Member
  • *****
  • Posts: 2287
Re: Table 19 BS 9999:2017
« Reply #5 on: January 28, 2017, 09:01:51 PM »
Lower than 11m is a four storey building why would you need a high reach appliance? Access is all about percentage of the building you can get to and the width of road, turning circles and such.
« Last Edit: January 28, 2017, 09:06:06 PM by Tom Sutton »
All my responses only apply to England and Wales and they are an overview of the subject, hopefully it will point you in the right direction and always treat with caution.

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: Table 19 BS 9999:2017
« Reply #6 on: January 28, 2017, 09:51:06 PM »
The rule is for large storage buildings Tom where for some reason there is seen to be some need to spray water onto roof sheeting the benefit of which has always defeated me!

Offline Fishy

  • Hero Member
  • *****
  • Posts: 777
Re: Table 19 BS 9999:2017
« Reply #7 on: January 30, 2017, 08:56:32 AM »
Not sure why mean roof height is a particular issue for large storage buildings?  In any case, Table 19 looks like a simplified version of Table 21 in the 2008 version, which didn't recommend high-reach access for buildings <11 m high either.

Offline Revol

  • Jr. Member
  • **
  • Posts: 71
Re: Table 19 BS 9999:2017
« Reply #8 on: January 30, 2017, 08:15:31 PM »
Not sure why mean roof height is a particular issue for large storage buildings?  In any case, Table 19 looks like a simplified version of Table 21 in the 2008 version, which didn't recommend high-reach access for buildings <11 m high either.
Fishy, table 21 in the 2008 doc does provide guidance on the percentage of perimeter access to be provided by a high reach appliance to buildings over 11m. The new table has had the column describing the type of appliance omitted ...