Thanks Fishy diagrams 1 & 2 with B1 told me what I need to know but as it appears FD20 door do not exist and you have to used FD30 doors so why ask for them?
From a little research I found the following.
The Building Regulations Approved Document B identifies minimum fire resistance periods for various elements of construction, including fire doors. The guidance recommends doors with a fire resistance period of 20 minutes (FD20) in some instances, and 30 minutes (FD30) in others.
In the distant past, it was possible to obtain a fire door that had a dual classification. Following a test, this door design could be accepted as an FD30 if installed with intumescent seals, and as an FD20 if installed without seals. In developing the BWF-CERTIFIRE Fire Door and Door Set Scheme in 1995, the BWF and the fire door manufacturers noted when testing dual rated doors that, in order to meet an FD20 rating without intumescent seals, the door had to be fitted very accurately into its frame, with little margin for error. This would be difficult to achieve consistently on site. Furthermore, this accurate fit would have to be maintained during the service life of the door assembly.
This reliability could only be achieved with doors fitted with intumescent seals; the safe practice is to have side and top edge seals in place for both FD20 and FD30 requirements. It was decided from the Scheme?s inception that its door manufacturing members would no longer test and sell an FD20 fire door except with intumescent seals fitted. Typically this determines that an FD30 product is in fact used for both levels of performance.