If you needed 60 mins or less, you could potentially use BS 5268-4.2: 1990 (withdrawn, but still useful), assuming that the lath and plaster provides no contribution. There's nothing similar for 90 mins+, though. The other useful source is BRE's "Guidelines for the construction of fire-resisting structural elements" by Morris, Read and Cooke, but again this doesn't cover anything over 60 mins, nor does it assign any F/R to timber lath ceilings (only expamet lath).
Beware as well ceilings tested only to BS 476: Part 23 - they're not suitable for use as protection to timber floors. You do need to remember that a floor is a load-bearing construction, so the F/R will depend upon the size of the joists, as well as the floorboard type and thickness.