Author Topic: BS 476-22 - No longer acceptable for external fire rated doors?  (Read 3300 times)

Offline Suttonfire

  • Full Member
  • ***
  • Posts: 130
The following indicates that a fire door tested to BS 476-22 can no longer be accepted for an external fire door, i.e. a door which opens onto a balcony with a single direction of travel in a block of flats: https://www.robust-uk.com/new-ce-marking-regulations-for-external-fire-rated-doors/?utm_content=buffer85944&utm_medium=social&utm_source=facebook.com&utm_campaign=buffer

Is this correct? I can see no mention in the MHCLG guidance issued in 2020 of BS 476-22 not being a suitable standard for fire doors which open externally.

Offline AnthonyB

  • Firenet Extinguisher Expert
  • Global Moderator
  • Hero Member
  • *****
  • Posts: 2480
    • http://www.firewizard.co.uk
Re: BS 476-22 - No longer acceptable for external fire rated doors?
« Reply #1 on: April 15, 2021, 07:28:47 PM »
It means nothing long term unless the UKCA system maintains the status quo after CE ceases to apply in a few months - although it looks like this should have been enforced for over a year on new installations. It doesn't appear retrospective.
Anthony Buck
Owner & Fire Safety Consultant at Fire Wizard


Extinguisher/Fire History Enthusiast

Fire Extinguisher Facebook Group:
http://www.facebook.com/group.php?gid=65...415&ref=ts
http://www.youtube.com/user/contactacb
https://uk.linkedin.com/in/anthony-buck-36

Offline Suttonfire

  • Full Member
  • ***
  • Posts: 130
Re: BS 476-22 - No longer acceptable for external fire rated doors?
« Reply #2 on: April 16, 2021, 08:31:20 PM »
Thanks, could I clarify - would a new fire rated door be permissible to a flat which opened on to a balcony (single direction of travel) if it complies to BS 476-22?

Would it just be the case that the door could not be CE marked, but would still considered to be suitably fire resisting based on compliance to the BS? Thanks
« Last Edit: April 16, 2021, 08:37:07 PM by Suttonfire »