Author Topic: Unprotected floor  (Read 3404 times)

Offline lyledunn

  • Hero Member
  • *****
  • Posts: 503
Unprotected floor
« on: August 05, 2021, 09:16:41 PM »
Small 3storey bar with basement used only for keg storage. Bar floor over basement has exposed joist throughout. Been that way since the bar was constructed 50 years ago. Following some incidental alterations BC have indicated that they will require fire protection to the floor or comprehensive ASD coverage in the basement.
I don?t dispute the merits but I do feel that maybe they are stepping beyond their authority given that the BC application did not involve works to the basement.

Offline AnthonyB

  • Firenet Extinguisher Expert
  • Global Moderator
  • Hero Member
  • *****
  • Posts: 2480
    • http://www.firewizard.co.uk
Re: Unprotected floor
« Reply #1 on: August 06, 2021, 08:31:40 PM »
NI Building Regulations look like they can have greater scope on alterations than the E&W ones so could be interpreted to allow this requirement(rightly or wrongly). Besides if they are concerned they could just pass it over to NIFRS who would simply use the The Fire Safety Regulations (Northern Ireland) 2010, I'm aware of cases where FRS have take action against unprotected basements in existing premises.




Application to alterations and extensions
7.?(1) Subject to the provisions of regulation 4, Parts A to L and Parts R and V shall apply to?
(a) a structural alteration or extension of an existing building; and
(b) the existing building as affected by that alteration or extension to the extent (subject to the
provisions of regulation 8) of prohibiting any alteration or extension which would cause a
new or greater contravention of any regulation.
(2) In applying the regulation under paragraph (1)(a), the alteration or extension shall be treated
as if it were part of a building being newly erected identical to and to be used for the same
purposes as the building as altered or extended.
(3) In determining for the purposes of paragraph (1)(b) whether the alteration or extension
would cause a new or greater contravention of any regulation, the following provisions shall
apply?
(a) the regulations shall be applied in each of the following ways?
(i) to the building as altered or extended treated as if it were being newly erected in its
proposed form for the purposes for which it will be used when altered or extended;
and
(ii) to the existing building treated as if it were being newly erected in its existing form
but for the purposes for which it will be used when altered or extended; and
(b) the alteration or extension shall be regarded as being such as would cause a new or
greater contravention if (when the regulations are applied as directed in sub-paragraph
(a)) the building as altered or extended?
(i) contravenes any regulation which does not apply to the existing building;
(ii) contravenes any regulation which is satisfied by the existing building; or
(iii) contravenes to a greater extent any regulation which is contravened by the existing
building.
Anthony Buck
Owner & Fire Safety Consultant at Fire Wizard


Extinguisher/Fire History Enthusiast

Fire Extinguisher Facebook Group:
http://www.facebook.com/group.php?gid=65...415&ref=ts
http://www.youtube.com/user/contactacb
https://uk.linkedin.com/in/anthony-buck-36

Offline lyledunn

  • Hero Member
  • *****
  • Posts: 503
Re: Unprotected floor
« Reply #2 on: August 06, 2021, 09:48:57 PM »
Yes Anthony,  I think the argument that BC are outside their remit would be a weak one. In any event, it can only be a good thing that fundamental fire safety considerations are appropriately in place in a building.