Author Topic: ladder in external escape route  (Read 3406 times)

Offline mosh

  • Newbie
  • *
  • Posts: 31
ladder in external escape route
« on: August 23, 2023, 07:32:48 PM »
Are ladders acceptable in external escape routes?

I have seen a 5-storey office block, with an office that occupies the 2 top floors (third and fourth floors). Exit from the office is only via the third floor, but they have a small roof terrace (on the roof above the fourth floor), with a ladder (about 6 -7 rungs going up over a wall, and then a small landing and then a ladder going down again the other side of the wall) that leads to the roof of the neighbouring block, which they can access as an alternative route.

I understood that ladders are no longer acceptable - and this is a building that was only constructed about 3 years ago. They said that it was signed off under fire regulations after the building was completed.

Am I missing something?

Offline AnthonyB

  • Firenet Extinguisher Expert
  • Global Moderator
  • Hero Member
  • *****
  • Posts: 2480
    • http://www.firewizard.co.uk
Re: ladder in external escape route
« Reply #1 on: August 23, 2023, 08:57:51 PM »
Such torturous routes were very common last century as the only way in very old city centres (often found in London, Manchester, Leeds, Liverpool & Birmingham) of giving existing landlocked buildings a second MoE & was considered better than nothing, along with hatches and doors in party walls, etc.

However guidance has been set against this sort of thing for a long time and the FP Act guides deprecated them too.

Having said that even current guidance accepts ladders, etc - but only in exceptional circumstances.

ADB
Fixed ladders should not be provided as a means of escape for members of the public. They should only be provided where a conventional stair is impractical, such as for access to plant rooms which are not normally occupied.

DCLG/HO
While not normally acceptable, the use of ladders, floor hatches, wall hatches or window exits may be suitable for small numbers of able-bodied, trained staff in exceptional circumstances. (more or less mirroring the FP Act guide other than a prescriptive number which I believe used to be 5 without digging them out)

So I would ask - who are they expecting the route to be used by?

"signed off under fire regulations" implies, as we don't have fire certificates, that either they are fibbing or the broken building control process has just cracked again if this has been accepted for a normal escape for building occupiers as oppose to a plant room or similar (where they are common)
Anthony Buck
Owner & Fire Safety Consultant at Fire Wizard


Extinguisher/Fire History Enthusiast

Fire Extinguisher Facebook Group:
http://www.facebook.com/group.php?gid=65...415&ref=ts
http://www.youtube.com/user/contactacb
https://uk.linkedin.com/in/anthony-buck-36

Offline mosh

  • Newbie
  • *
  • Posts: 31
Re: ladder in external escape route
« Reply #2 on: August 24, 2023, 08:00:05 AM »
Thanks, Anthony, for your helpful reply.