Author Topic: pressure testing of FM200 cylinders  (Read 10568 times)

Offline Ashley Wood

  • Sr. Member
  • ****
  • Posts: 253
    • http://www.thermatech.uk.com
pressure testing of FM200 cylinders
« on: February 06, 2006, 01:10:34 PM »
Can anyone advise me as to the recommendations regarding pressure testing of FM200 cylinders. Also, what document details the recommendations?

Thanks

Offline AnthonyB

  • Firenet Extinguisher Expert
  • Global Moderator
  • Hero Member
  • *****
  • Posts: 2480
    • http://www.firewizard.co.uk
pressure testing of FM200 cylinders
« Reply #1 on: February 06, 2006, 11:17:41 PM »
Of the top of my head, bearing in mind the time of night, I would suggest that the BS for the type & construction of gas cylinder would be the way to go, hich normally has a table of test intervals for that type of cylinder and it's usage (i.e. gas contents & their application). Without looking I cannot be certain, but would bet that it is 10 years like cylinders of similar construction filled with CO2 for firefighting
Anthony Buck
Owner & Fire Safety Consultant at Fire Wizard


Extinguisher/Fire History Enthusiast

Fire Extinguisher Facebook Group:
http://www.facebook.com/group.php?gid=65...415&ref=ts
http://www.youtube.com/user/contactacb
https://uk.linkedin.com/in/anthony-buck-36

Offline David Rooney

  • Hero Member
  • *****
  • Posts: 891
    • http://ctafire.co.uk
pressure testing of FM200 cylinders
« Reply #2 on: March 22, 2006, 06:52:14 PM »
BS ISO 14520-1:2000      Gaseous fire-extinguishing systems. Physical properties and system design. General requirements

I think the pressure testing comes under part 3.

You should test every 10 years, after 20 years test every five.
CTA Fire - BAFE SP203 - F Gas Accredited - Wireless Fire Alarm System Specialists - Established 1985 - www.ctafire.co.uk
Natural Born Cynic

Offline AnthonyB

  • Firenet Extinguisher Expert
  • Global Moderator
  • Hero Member
  • *****
  • Posts: 2480
    • http://www.firewizard.co.uk
pressure testing of FM200 cylinders
« Reply #3 on: March 22, 2006, 11:06:12 PM »
From the General requirements maintenance section of BS ISO 14520-1

"9.2.2 Container
Containers shall be subjected to periodical tests as required by the relevant national standard."

Which would be evry 10 years as the old 20, 10, 5 regime was removed a few years ago when BS EN's replaced the old BS for steel & aluminium gas cylinder testing
Anthony Buck
Owner & Fire Safety Consultant at Fire Wizard


Extinguisher/Fire History Enthusiast

Fire Extinguisher Facebook Group:
http://www.facebook.com/group.php?gid=65...415&ref=ts
http://www.youtube.com/user/contactacb
https://uk.linkedin.com/in/anthony-buck-36

Offline Ashley Wood

  • Sr. Member
  • ****
  • Posts: 253
    • http://www.thermatech.uk.com
pressure testing of FM200 cylinders
« Reply #4 on: March 23, 2006, 08:07:00 AM »
Thanks guys for your help, very usefull.

VBR

Ashley