So what we really need is a double pole BGU that can be wired to break the supply to the lock, and to also signal the fire alarm system.
?
David you are exactly right.
My risk assessment for the premises ( see my post of 6 June) where I went for just a red bgu box, double pole of course, and staff training for fire and for incidents other than a fire has brought the following comment from the fire authority-
"The decision to install a red BGU only may create a hazard to the occupants of the building. In the event of a failure of the fire alarm they may be unable to exit the building. The risk assessment should be reviewed"
The alarm is L1 to the current 5839. For events other than fire there are exits at remote ends of the building without any mag locks. (The building which in this case is 200m long). The intermediate fire exits are secured on mag locks linked to the fire alarm and a panic bolt. The red bgu operates the fire alarm, if people follow their training their first action is to sound the alarm, if not already sounding. The alarm will release the mag lock and so only one action will be necessary to open the door- ie the panic bolt.
I had not considered a total failure of the fire alarm system which would prevent the alarm operating but would maintain the power to the mag lock but Davids suggestion would cater for this event.
Do you think the fire authority are being reasonable in this case?