Hi Wee Brian
How would you feel about explaining hw the new approach actually works?
I believe what you say of course but I do like to understand it as well.
I accept the objective is to keep the stair clear by ensuring that the adjoining lobbies or corridors are at a slightly lower pressure so any flow is from stair to corridor.
I would have expected a vent at the head of the stair to be an outlet because of the stack effect- the air temperature at the top will be warmer than than the air outside so warm air will flow out of the the vent and cooler air from outside will enter at a lower level if it can get in. And if make up air cant get in then the outflow will be affected and reduced. So I cant see how a vent at the top can be an inlet?
The AOV in the corridor is there to ensure that any bouyant hot smoke vents to outside rather than building up a pressure and passing into the staircase, and as a bonus the smoke layer in the corridor will also be kept at a higher level making conditions a little more tenable than otherwise. I also accept the BRE report and parameters based on a 250kw fire and a flat door slightly ajar even though I am not convinced that this is the most likely scenario. In many cases I think the smoke will be cooler.
Whilst the objective is not to clear the lobby of smoke, only to reduce the pressure that would otherwise push smoke into the stairway, surely the AOV will only be partially efficient because without inlet air the best it can achieve is a neutral plane, there will be inertia, pulsing, and if the outflow is substantial it is bound to entrain air against the flow increasing the smoke volume and causing smokelogging further back in the lobby.
There is no flow from the stair into the lobby unless the door is open.
Now, please Brian where have I got this wrong?