In this scenario, I am assuming that the sounders on floor that didn't pulse are connected to one networked panel but the MCP initiating the alarm was connected to a different networked panel.
Whilst most networked systems, that I have experience of, operate by having the same operation software configuration stored in each network node of the system, if you lose the connection between panels, cause and effect functions initiating on one panel but requiring an operation on another panel, might not work.
The simple fact is that if you lose the connection between two panels (nodes) then the signal initiated from the first panel cannot be seen by the second panel. Therefore, even if the programme in the second floor was configured for pulsed alarms on receipt of an alarm condition from a device on another network node, if it doesn't receive the signal then it can't initiate it's function programmes because it doesn't even know an alarm exists.
Therefore the panels haven't reverted to a different configuration because the network connection has failed, but simply because the initiating signal hasn't got through.
Networks should be a loop and capable of transmitting in both directions around the loop to avoid a simple disconnection at one point causing a failure of operation
In this scenario, the loss of the network in any form should have been indicated on all other networked panels as a fault and the user should have been aware that this was a serious fault that could have serious consequences to the operation of the alarm.
If no fault was showing, it must be that the configuration programmes in all other working panels was incorrect and not even looking for the missing 'network node'.