« on: September 16, 2004, 12:54:15 PM »
When in a job you reach your Whistle time (according to the B.A. Board) and you still have a reading of say 120 bar, Is it permissable to stay in the job as long as you have radio contact with BAECO.

I have been told this is the case,as it would be a waste of air to come out of the job with a half full cylinder. Although I understand this, I don't see how the BAECO can be in control of his board, if the wearers are making up their own working limits.

Any guidance appreciated.

Guest

  • Guest
B.A. Whistle time
« Reply #1 on: September 16, 2004, 01:27:38 PM »
Is your query based on actual experience of this occurring or is it seeking clarification of a hypothetical situation based on an anomoly within the TB.
Either way if i were OiC or ECO I would insist on your withdrawal. For the wearer to go beyond their t.o.w the ECO no longer has complete control over the details on the board. Therefore in spite of the possibilty of the wearer staying in there is the possibility for confusion on the part of the ECO.
IF IN DOUBT GET THEM OUT. :shock:  :shock:

Offline Giovanni

  • Newbie
  • *
  • Posts: 16
B.A. Whistle time
« Reply #2 on: September 16, 2004, 01:34:16 PM »
Ba wearers should be back at BA control before the whistle sounds, all timings must be by the BAECO. Duration tables are worked out at a person walking at 4 miles/hour so the chances of the BAECO's time of whistle being before the wearers actual whistle activation are slim unless of course the wearer is not doing any work! All BA wearers as a matter of good practise and training should be aware of their durations and their available time to continue and this will vary from person to person e.g. lung capacity, physical exertion, distance from control and other factors.
This sounds like a very poor and dangerous practise.
Gio :o

Offline Steve Mc Queen

  • Newbie
  • *
  • Posts: 9
B.A. Whistle time
« Reply #3 on: September 17, 2004, 01:30:14 PM »
I understand how the t.o.w is worked out, but on many occasions(mainly during drills,with small work loads) wearers reach their t.o.w. with plenty of air remaining.
It is in these situations where the only indication a wearer has of his work duration is his contents gauge, if he is doing little work, it is easy for him to pass his t.o.w. without him knowing (gauge still reading high due to low work rate). If b.a.e.c.o.contacts him via radio and informs him he should be out, say in 5 mins and he has 120 bar remaining is he permitted to stay in the job untill his air is approching actual whistle time?

I have been told that this is acceptable, I find that difficult to agree with and am of the opinon that it leads to b.a.e.c.o having no control over his wearers.

As far as I canm see this is not covered in 1/97

Guest

  • Guest
B.A. Whistle time
« Reply #4 on: September 20, 2004, 07:01:40 AM »
I was told during basic; that if the BA team leader is contacted by the ECO. He can/should make an assessment of the workload; check his team member’s gauge reading and then make a decision whether to continue the task or withdraw.

During a training drill on station, we had a situation where this was put in the scenario and consequently the experienced ECO got a little bit annoyed when his request to withdraw was ignored by a less experienced guy. The up shot was, training were contacted and they said the BA team leader was right, but the ECO should always remind them they were reaching the time of whistle.

Offline pugh

  • Jr. Member
  • **
  • Posts: 63
B.A. Whistle time
« Reply #5 on: September 23, 2004, 10:37:56 AM »
:D
New technology, i.e. telemetry, might make this thread redundant as the new Draeger system updates whistle times according to wearer breathing rates.Damned clever stuff, what?

 Might even result in a revised 1/97.
 :D

Offline Steve Mc Queen

  • Newbie
  • *
  • Posts: 9
B.A. Whistle time
« Reply #6 on: September 23, 2004, 04:24:35 PM »
pugh
Are any Brigades using this eqt yet? or is it still being developed?

Offline fireftrm

  • Hero Member
  • *****
  • Posts: 673
B.A. Whistle time
« Reply #7 on: September 27, 2004, 10:21:35 AM »
http://www.draeger.com/ST/internet/UK/en/Industries/Fire/Operations/Monitoring/PSS_Merlin/op_pss_merlin.jsp

Draeger Merlin is already out there, been in plenty of FRS magazines too. I believe that it is in use at a couple of UK FRS and plans for some more soon. I am not sure but I think N.I. are using it............
My posts reflect my personal views and beliefs and not those of my employer. If I offend anyone it is usually unintentional, please be kind. If it is intentional I guess it will be clear!

fire032

  • Guest
B.A. Whistle time
« Reply #8 on: February 24, 2005, 10:02:08 PM »
It's nice to know that your BAECO is watching out for you, however, "If" you are in radio contact with the BAECO and you can let him know what's going on inside then there should be no problem and you should carry on with your task. Ideally, you should be coming out of the job with 55 bar (+/- 5 bar) irrespective of the time.

The problems start to arise when your BAECO cannot get hold you and you are at your 'Time of whistle' on the BA board. Then he has to make a decision.

Personally, if I was the ECO and 'my team' did'nt come out at the time of whistle (according to the BA board) and I couldnt get hold of them via radio or any other means- I would instigate a BA EMERGENCY. Send in the emergency teams, inform the OIC and inform Brigade Control. Brigade Control will then send reinforcements and Officers. It's a big responsibility for the BAECO ( he might even be inexperienced regarding ECO's duties or 'the new boy') and it takes a brave man to call a BA Emergency-But hey.....They're our mates in there..Let's air on the side of caution, sod the consequences regarding instigating a BA Emergency and look after our own....You may get a bollocking for getting an officer out of bed at 2 in the morning but at least you DID THE RIGHT THING- to make sure that your mates are safe and that they are going home to their families in the back of the big red truck with you & their 'friends'.

Offline Simon Morriss

  • Jr. Member
  • **
  • Posts: 68
B.A. Whistle time
« Reply #9 on: March 02, 2005, 08:17:35 AM »
I can believe I am reading this!!!!

The TOW is your safety margin, you should never eat into this unless you are having a problem.

Steve McQueen I hate to suggest but is some one pulling your leg here.  If you are instructed to work beyond your TOW is if pure negligent on the part of the OIC and you should never agree to do so.  Your life and safety are the most important thing at all times.

Simon

Offline burgermuncher999

  • Jr. Member
  • **
  • Posts: 50
B.A. Whistle time
« Reply #10 on: March 02, 2005, 09:43:58 AM »
Here, here. Erosion of safety standards in this manner only feeds a generic management culture that would happily acknowledge the risk of an employee dying in a situation that might otherwise be preventable through investment in BA telemetry or enhanced training for those who believe such dangerous practices to be acceptable. Other Ffs have died in the past and the net gain of their deaths were BA control procedures, low pressure warning devices, fire behaviour training, ppv etc etc. Respect those who have gone before us and use the procedures and equipment in the manner they were intended for. To fail to do so is to say that Firefighters in the past have died in vain and the lessons learnt have either fell on deaf ears or long since been forgotten.

Offline Acco

  • Newbie
  • *
  • Posts: 10
B.A. Whistle time
« Reply #11 on: May 10, 2005, 02:44:35 PM »
40lPm is the average rate of oxygen used in the time of work by a fit individual. Some use more some less. But consider your crew you maybe on 120bar what does the rest of the crew read. I personally think that the standard of reenering a building of no less less than 80% of max capacicity ie 200bar entering at 160bar is about right -  except under exceptional circumstances.

Use commonsence as well as procedure time recal  is
Fire032  and burgermuncher999 is correct use commonsence, experiance and instintic as a guide.

justso

  • Guest
B.A. Whistle time
« Reply #12 on: May 10, 2005, 11:18:13 PM »
i think everyone is confused by the use of t.o.w i hope that what steve is actually talking about is his turnround time which is something completely differant .

Offline fireftrm

  • Hero Member
  • *****
  • Posts: 673
B.A. Whistle time
« Reply #13 on: May 12, 2005, 02:24:02 PM »
I have recently  been in some disagreement with trainers over the TOW and turn round times. It appears that the teaching in BAI courses is that it is good air management to return to the BAECO with just over the safety margin pressure (60 bar as 55bar cannot be used - rounding up). They also state that if the whistle goes off before they get to the BA set off, but outside then they have done well. I have got to a slight compromise in that they accept that this is alright, but on the basis that 'you got away with it this time'. My opinion is that you should turn round once you have used half the available air for that wear, with riska assessment applied:

Thus 280 bar on entry, deduct 60 bar leaving 220 bar to wear. 110 to use on the way in and 110 on the way out. Thus turn round is the 110 plus the 60 safety giving 170. The smae for other readings but if the half is a figure ending in 5 round up the amount to come out with for safety (270 minus 60 = 210 /2 = 105 add 60 back in = 165 then round up to 170 gving turn round). This should be adjusted by the team if they have been using excessive exertion on the way in, for example hauling hose, and thus would use much less air on the way back. However, I beleive that the over riding principle should be to exit the building with more air not less and that being at, in, or even close to the safety margin is acting in a potentially unsafe manner.

Comments please and what about from BAIs/policy writers?

Maybe a consensus and a policy may appear form this discussion
My posts reflect my personal views and beliefs and not those of my employer. If I offend anyone it is usually unintentional, please be kind. If it is intentional I guess it will be clear!

Offline burgermuncher999

  • Jr. Member
  • **
  • Posts: 50
B.A. Whistle time
« Reply #14 on: May 12, 2005, 03:00:38 PM »
As a trainer i do agree that it is good practice for wearers to make use of as much of their working duration as is safely possible. This will greatly enhance their ability to carry out their brief effectively and reduce the number of personnel required to act as reliefs for crews who might exit the risk with a good per centage of the working duration still in the cylinder.
Common sense and not maths is what needs to be applied.
If a Firefighter enters a house fire with 200 bar then by the book their turnaround would be at 130 bar. Should they therefore come out of the risk if they are in the ground floor living room only 40 ft from the ECB and are familiar with the route to exit. I would say not. Provided they are confident in their ability to exit the building by the time of whistle i would say stay in and exit at a time when you deem it appropriate bearing in mind they MUST reach the board prior to actuation of whistle.
The use of PPV greatly enhances conditions of visibility and as such with PPV in use and the building ventilated i think it ridiculous for any crew to exit at the turnaround time when the travel time to the front door from any point in a standard 3 bed domestic may be as little as 3 mins. In this case they could turnaround at 130 on the 1st floor and be back at the board with 120 bar still in the cylinder.
I won't say they ain't playing it by the book but in doing so they are also failing to apply a degree of common sense and are reducing the effectiveness and efficiency of the OiC's available resources.
Turnaround time becomes more important in relation to deep penetration into a building which is unventilated and the risk of physical exertion and disorientation is present. In this case i would say start exiting at or about your turnaround time and be back to the board prior to actuation of whistle. However i would still say that to return to a board under such circumstances with too much air is not good practice.
Opinions will vary but i think 80 bar upon return to the board is a good practical figure. Others might disagree and i too am interested in hearing more.