The de-rating factor recommendation in BS5839 part 1 2002 is actually 1 or 1.75 and not 2.
It is 1 when the system alarm load is equal or less than 1/20th of the battery's stated capacity. It is 1.75 when the battery's alarm load is greater than 1/20th of the battery's staed capacity.
BS recommends that you check any de-rating factor to be used from the actual battery manufacturers literature. If none is available, you should use the figure 1.75.
Using a de-rating factor in your calculations provides a calaculation as taking into account of the fact that the battery's stated capacity in AH is a nominal figure because most batteries can't actaully meet their capacity rating on high loads and are likely to exceed it on low loads. I.e a 24AH would probably be able to provide 1A for 30 hours but only 8 hours at 2.4A. The battery capacity is normally rated as if 1/20th is being taken out of it i.e if 1.2A was taken from a 24AH battery it would last 20 hours (i.e what you would expect from a 24AH battery!)
In respect of the BS formula, I know that you, Benz, can cope with formula math because I've noticed that you quote it quite often in your posts. Not everyone is as proficient, and the formula shown in BS i.e.
1.25(T1 I1 + D I2/2) fazes many people.
In trying to calculate the likely duty of the battery in an installed system, there is a simpler way of making a good calculation.
At the end of the day, you are trying to prove that the installed battery capacity is sufficient for the system load and you want to know how many hours standby the battery can provide (normally 24 hours in L installations).
The Fire Alarm Wizard's own method and calculation of doing this is carried out as follows:
1) Determine the system batterys' rated capacity in AH by reading what is printed on the battery.
2) Convert that figure into mAH by multiplying by 1000. i.e a 7AH battery becomes 7000mAH
3) Take 75% of the figure calculated in 3 above ( i.e. 75% of 7000mAH is 5250mAH) This figure (5250 in this example) becomes the new available battery capacity to be used in further calculation.
4) Take readings of both the standby load (in mA) and alarm load (in mA) of the systems *. For our example we will assume that our readings give a standby load of 70mA and an alarm load of 200mA
5) We now deduct half the alarm load reading from the battery capacity figure (we use a reading of half because the alarm load only has to operate for 30 mins). In our calculation this would be 5250 - 100 = 5150. This figure of 5150 becomes the new available battery capacity figure to be used in further calculation.
6) Divide the standby load reading into available battery capacity figure. In our calculation this would be 5150/70 = 73.57
7) The figure of 73.75 now equates to the number of hours standby duty available in our battery whilst still providing sufficient capacity to sound the full alarm load for 30 minutes and assuming our battery only has 75% of it's rated capacity.
* The practical method of calculating standby and alarm loads is to connect a ampmeter (reading mA) in series with the battery connection of the control panel/power supply. Disconnect the mains supply to the control panel and then take the standby load reading. Then initiate a full fire condition and then take the alarm load reading.
I hope you will agree that the above is the simplest practical method for an engineer on site to calculate the available standby capacity of battery in hours of any installed system and turns the BS 5839 formula into a set of practical and simply understood steps. Please note however that this method and calculation does not factor in any battery de-rating factor. I have never included the de-rating factor into my method because a) The de-rating figure is often 1 and therefore has no effect on the calculation and b) because it adds a further step to the calculation that blow's most fire aalrm engineer's minds! You could probably cope with it and adjust Wiz's on-site calculation method and include it.