I thought I would run this one by you all,
This is a purpose built six storey block constructed of concrete walls, floors, and ceilings located in a less than desirable area , housing tenants from all walks of life.
It was constructed in the early 70's and has passed fire brigade inspections in it's past.
The FRA has stated that a fire alarm system is not required within the common areas as the on going vandalism of the block on a daily basis would include the vandalism of the fire alarm system rendering it useless if it were required in a emergency.
The FRA states that each individual flat requires mains wired detection and with a minimum of a 30 minute fire resisting door leading on to the escape route.
Looking at the RRFSO article 8 -duty to take general fire precautions (a) & (B) and Article 4 (1) (e) means of detecting fire on the premises and giving warning in case of fire to relevant persons is the block conplying or not complying?
Surely if a alarm system is installed and then vandalised its still not complying as it is no longer fit for purpose if it is not repaired. If the alarm was monitored the fire service would attend every day and i'm sure they would not want that.
In a nutshell, in a court of law would the FRA be deemed suitable and sufficient although technically the above articles do not seem to have been met?
I would welcome everyones views..
Many thanks
I work in social housing so deal will the same issue a lot. The vast majority of all our blocks are purpose built and typically of concrete construction. We do not have detection or alarms in the communal areas of these blocks. BS5588-1 and CP3 part 4 1971 specifically says that these are not required in flats and maisonettes as stay put is fine and recommended - like you said, an alarm panel would be vandalised.
We aim to ensure that all flats have 30 minute fire doors to protect the means of escape (this will take time to bring all doors up to this standard as many are not but we have an agreed timescale which the fire brigade are happy with). The inside of each flat is not covered by the RR(FS)O as it is a domestic dwelling so although it would be ideal, it is not our responsibility to provide hard wired smoke detection to each dwelling. This is the responsibility of the resident (the fire brigades can give out smoke detectors and install these for free). We also try and keep the communal areas free from combustibles and paint the walls/ ceilings with class 0 paint to avoid fires starting in the communal areas therefore not needing an alarm.
With your enforcment notice, if the building you describe has a lift or more than one staircase, it may be necessary to have directional signage to point to the stairs as most residents would normally use the lift or the usual stairs they use. If not, and only 1 staircase with 2 exits seen from bottom of stairs....is signage really needed?
Emergency lighting should be installed in buildings over 18m according to BS5588-1 so will be needed.