Author Topic: Apollo Discovery read/write  (Read 9386 times)

Offline Wiz

  • Hero Member
  • *****
  • Posts: 1591
Apollo Discovery read/write
« on: March 19, 2009, 01:52:17 PM »
Hi Guys,

Has anyone had any issues with the read/write element of Apollo Discovery manual call points manufactured in the last two years?

Offline Allen Higginson

  • Hero Member
  • *****
  • Posts: 1131
Re: Apollo Discovery read/write
« Reply #1 on: March 19, 2009, 03:59:36 PM »
Hi Guys,

Has anyone had any issues with the read/write element of Apollo Discovery manual call points manufactured in the last two years?
Lost me there Wiz??

Offline Buggy

  • Newbie
  • *
  • Posts: 18
Re: Apollo Discovery read/write
« Reply #2 on: March 19, 2009, 04:17:19 PM »
Im in the same boat as Buzz. I thought it was only Discovery detectors had a 'memory' facility.  ???

Graeme

  • Guest
Re: Apollo Discovery read/write
« Reply #3 on: March 19, 2009, 05:16:56 PM »
Wiz

The only thing i had an issue with was the led blink on poll option did not work on them.


Graeme

Offline Wiz

  • Hero Member
  • *****
  • Posts: 1591
Re: Apollo Discovery read/write
« Reply #4 on: March 19, 2009, 06:12:24 PM »
Thanks guys for responses so far.

Buzz - No problem being lost, mate!. If you had suffered the read/write problem you would have known about it!

Buggy - All the Discovery devices have the Ram.

Graeme - Thanks for response.

Anyone else have anything to add?

Offline dark one

  • Newbie
  • *
  • Posts: 25
Re: Apollo Discovery read/write
« Reply #5 on: March 19, 2009, 07:18:28 PM »
never had any problems with callpoints only with detectors

Offline Wiz

  • Hero Member
  • *****
  • Posts: 1591
Re: Apollo Discovery read/write
« Reply #6 on: March 20, 2009, 09:51:16 AM »
dark one, are you able to confirm what problems you had and, most impoeratntly, the manufacture of the control panel on the system?

Graeme

  • Guest
Re: Apollo Discovery read/write
« Reply #7 on: March 20, 2009, 03:54:11 PM »
Wiz

There was a fault with Disco detectors in that the machine used to make the mouldings was fractionally out so i as found out heads would not meet up fully with the address cards in the base and it caused devices to take another address and cause double address and device missing faults.

Offline Wiz

  • Hero Member
  • *****
  • Posts: 1591
Re: Apollo Discovery read/write
« Reply #8 on: March 20, 2009, 05:55:57 PM »
Graeme, That is not the fault I am most interested in, but could you please tell me the approx. dates when you suffered the problem you descibe.

Offline dark one

  • Newbie
  • *
  • Posts: 25
Re: Apollo Discovery read/write
« Reply #9 on: March 20, 2009, 08:18:45 PM »
wiz reports at the panel as maintenance fault only on kentec synco panels have to replace head and hard reset panel to clear

Graeme

  • Guest
Re: Apollo Discovery read/write
« Reply #10 on: March 25, 2009, 07:59:09 PM »
Graeme, That is not the fault I am most interested in, but could you please tell me the approx. dates when you suffered the problem you descibe.

roughly two years ago

Offline dark one

  • Newbie
  • *
  • Posts: 25
Re: Apollo Discovery read/write
« Reply #11 on: March 28, 2009, 08:30:53 PM »
have had email from kentec this week telling us there is a problem with firmware version V5.93
that gives bad data faults and device type faults on apollo devices don't know if this is relevant to you but this sort of thing is always useful to know.  A fimware update is needed ???.