Re: BS 9999 -Fire Safety Manual - Regulation 16B
« Reply #30 on: July 17, 2009, 01:39:04 PM »
CivvyFSO
Thanks for that
 ???
Not so confused still in a big world

Offline rn976

  • Newbie
  • *
  • Posts: 32
Re: BS 9999 -Fire Safety Manual - Regulation 16B
« Reply #31 on: July 20, 2009, 10:21:12 AM »

CivvyFSO


just a quick question re the AI and ADB can you let me know where this interpretion has come from as massive debate now going on and its difficult to hear the cricket scores

many thanks

confused in a big world  ???

Offline CivvyFSO

  • Hero Member
  • *****
  • Posts: 1583
Re: BS 9999 -Fire Safety Manual - Regulation 16B
« Reply #32 on: July 20, 2009, 11:39:28 AM »
Try this link: http://www.communities.gov.uk/documents/housing/pdf/465607.pdf

That gives information regarding appeals and determinations. There is not much to debate about it. :)

Just to clarify the point about ADB: ADB is issued only as 'guidance' to assist persons to comply with the building regs. Any variation from ADB (even a full engineering solution) can be assessed by a BCO or an AI as to whether, in their professional opinion, it still meets the requirements of the regulations. It is any disagreement at this point that could give rise to a determination, which will have to go to the Secretary of State.

An appeal is very different and you should read the link posted above for information regarding this.

Offline rn976

  • Newbie
  • *
  • Posts: 32
Re: BS 9999 -Fire Safety Manual - Regulation 16B
« Reply #33 on: July 20, 2009, 12:17:51 PM »
To CivvyFSO
once again many thanks
 
knowing someone who knows where to look

Priceless

confused in a big world  :)