Thanks for your replies
Mike
the stores down one side of the Service Corridor are on the ground floor....there is another store on the second floor of approx 25 Sq m which is protected by 60 minutes fire doors that lead to a hospital street
Terry
what the fire service are saying is that the lift doors need to be lobbied so if there is a fire in the stores area the staff member in the service lift would not walk straight into it. The ground floor corridor obviously termonates at both ends with fire doors but the lift itself opens into it.
They have given the option of smoke control...to me though someone would still walk into the fire area even with smoke control.
Mushy. I have to get on my soap-box here. I'm an inspecting officer, and I think instances like this just damage our reputation.
It really annoys me when I hear Fire Authorities requesting things over and above what is reasonable. You have a premises that appears to be code compliant (within the scope of this discussion). And also have, what is shortly to be, an L1 system. Any fire that may break out in that store would be detected and the alarm raised. The ONLY circumstance that a person in the lift could possibly be affected is if the fire started when you were already in the lift (unless the person ignored the alarm. but that’s another matter). In a building of 3 floors (you said 2nd was the top floor), by the time you got to the second floor its not exactly going to be a raging inferno or totally smoke logged. So where is the significant risk to relevant persons? Additionally, the corridor you mentioned on the ground floor has a route out at either end (I am assuming this from your indication of fire doors at either end of the corridor) and is within a service area. So it isn't a protected corridor.
Sure, if the opportunity is there to interface the lift to bring it to ground, then I would say take that opportunity regardless of this matter. Its sound practice that will prevent person using the lifts in an emergency.
If you did this, the fire authority couldn't argue. They wouldn't have a leg to stand on.
Having said that I don't think they have much of a case anyway. My response to them would be;
I have reviewed my fire risk assessment and have taken into account the following matters.
1. A person would only be affected if he was already in the lift at the point the fire was detected.
2. The fire loading in the store does not pose a risk of rapid fire spread (I am assuming this is correct. if there are dangerous substances stored in there, this whole argument falls down).
3. Any storage is located at a suitable distance away from the lift doors.
4. The premises are covered by an L1 system.
5. This is a goods lift, and is only used by staff.
6. The lift is already code compliant, as every lift door to each floor provides 30 min FR. achieving the 60min horizontal compartmentation requirements for institutional premises. (i would be surprised if this is not the case in a hospital)
7. The ground floor corridor is not a protected corridor.
The findings from our review consider there is no significant risk of death or serious injury to relevant person, and therefore additional compartmentation is not required. Additionally, this is backed up by good management and our robust training regime of staff in both fire awareness and evacuation drills.
Can I ask? Is their request the result of an audit? Have they served you a notice? If so what article did they address this in?