Author Topic: Door Stop Size  (Read 9251 times)

Offline Suttonfire

  • Full Member
  • ***
  • Posts: 130
Door Stop Size
« on: October 31, 2017, 07:27:02 AM »
Please could anyone confirm whether a fire resisting door set, if fitted with intumescent strips and cold smoke seals, still requires a 25mm door stop?

My research into this has lead me to contradictory findings. Thanks

Offline nearlythere

  • Hero Member
  • *****
  • Posts: 4351
Re: Door Stop Size
« Reply #1 on: October 31, 2017, 10:07:58 AM »
Please could anyone confirm whether a fire resisting door set, if fitted with intumescent strips and cold smoke seals, still requires a 25mm door stop?

My research into this has lead me to contradictory findings. Thanks

The provision of Int and SS meant that the 25mm door stop glued and screwed was no longer necessary.
Double swing FR doors don't need stops provided the Int and SS are fitted.
We're not Brazil we're Northern Ireland.

Offline Mar62

  • Full Member
  • ***
  • Posts: 207
Re: Door Stop Size
« Reply #2 on: October 31, 2017, 03:57:22 PM »
Minimum of 12mm
Each and every day is a learning curve and today is one of those days?

Offline colin todd

  • Hero Member
  • *****
  • Posts: 3473
  • Civilianize enforcement -you know it makes sense.
    • http://www.cstodd.co.uk
Re: Door Stop Size
« Reply #3 on: October 31, 2017, 09:42:09 PM »
If it was tested with a 25mm stop, it will need a 25mm stop.
Colin Todd, C S Todd & Associates

Offline col10

  • Jr. Member
  • **
  • Posts: 85
Re: Door Stop Size
« Reply #4 on: November 01, 2017, 09:11:34 AM »
One of the manufacturers told me that the 25mm stop aids capillarity action and providing strips and seals are fitted the 12mm stop is better.

Offline Fire Monkey

  • Full Member
  • ***
  • Posts: 176
Re: Door Stop Size
« Reply #5 on: November 01, 2017, 09:47:39 AM »
Are the doors original to the frames and are they a 'set'? As Colin says the door and frames need to be a tested system. You could find one fire door that required 25mm stops (or an inch in old money) and another that was design not to need stops so wide. What do the specs for the door say (should such information be available).