Author Topic: Batteries calculation ?  (Read 99756 times)

Offline Benzerari

  • Hero Member
  • *****
  • Posts: 1391
    • http://benzerari.tripod.com/fas/
Re: Batteries calculation ?
« Reply #135 on: April 04, 2009, 08:11:41 AM »
Benz,

I think you'll find that the current Gent Vigilon only has one set of batteries...


So what are the inputs of B1 and B2 into the back PCB board, on the top right hand corner then? aren't they come of two separate sets of batteries?

Offline Allen Higginson

  • Hero Member
  • *****
  • Posts: 1131
Re: Batteries calculation ?
« Reply #136 on: April 04, 2009, 09:32:29 AM »
Benz,

I think you'll find that the current Gent Vigilon only has one set of batteries...


So what are the inputs of B1 and B2 into the back PCB board, on the top right hand corner then? aren't they come of two separate sets of batteries?
So long since I looked in one but doesn't each battery have it's set of terminals?

Offline Benzerari

  • Hero Member
  • *****
  • Posts: 1391
    • http://benzerari.tripod.com/fas/
Re: Batteries calculation ?
« Reply #137 on: April 04, 2009, 07:49:33 PM »
Benz,

I think you'll find that the current Gent Vigilon only has one set of batteries...


So what are the inputs of B1 and B2 into the back PCB board, on the top right hand corner then? aren't they come of two separate sets of batteries?
So long since I looked in one but doesn't each battery have it's set of terminals?

Indeed is not each battery has its set of terminals, it's rather 2 batteries as one set supplying 24Vdc to terminal B1 in the PCB board, and 2 other batteries as one set supplying 24Vdc to terminal B2, thus two inputs from two different sets of batteries.

Offline Ark Angel

  • Jr. Member
  • **
  • Posts: 51
Re: Batteries calculation ?
« Reply #138 on: April 04, 2009, 08:02:05 PM »
Benz,

When I said the current vigilon, I meant the 6 loop. This has a different PSU to the older Vigilon and utilises only one set of batteries which are now housed in the panel instead of a seperate battery box....
The World Favours the Brave

Offline Benzerari

  • Hero Member
  • *****
  • Posts: 1391
    • http://benzerari.tripod.com/fas/
Re: Batteries calculation ?
« Reply #139 on: April 04, 2009, 08:08:07 PM »
Benz,

When I said the current vigilon, I meant the 6 loop. This has a different PSU to the older Vigilon and utilises only one set of batteries which are now housed in the panel instead of a seperate battery box....

Still the issue with BAFE requirement in regards to the so called old Vigilon 4loops and 2loops, how the 70% capacity requirement is defined, per set of batteries or their sum?